Ecmweb 7409 Arc Flash Pr
Arc Flash Clothing Labeling Requirements
May 18, 2015
Does your arc flash clothing and PPE really provide the proper level of protection?
Photo 1. One of the first arc flash protective suits made available in the market in the late ’70s and early ’80s.
In the late ’70s to early ’80s, the first arc flash suits began to appear on the market (Photo 1), most of which were made from double-layer 6 oz/yd2 meta-aramid and featured polycarbonate (plastic) windows for the face shield. These suits were considered state-of-the-art until 1996 when arc testing of clothing and PPE began.
However, it didn’t take long for the shortcomings of this type of arc flash protection clothing and PPE to become evident, especially at higher values of incident energy. During arc flash testing, it was found that the polycarbonate window would actually fail at a very low value of incident energy (approximately 1.5 cal/cm2), causing it to melt. These clear face shields have no arc rating. If you examine the garment label (click to see Photo 2), you’ll also see it lacks the required markings (ATPV, ASTM F1506, and NFPA 70E).
Clothing that has an arc rating but doesn’t comply with today’s labeling requirements is not considered arc-rated. An arc rating by itself does not necessarily indicate compliance with the required national standards, and the company using it may be at risk for citation from OSHA.
Photo 3a (click here to see Photo 3A) shows the label from a garment that seems to have an arc rating, but the label inside (Photo 3b) only states the garment meets NFPA 2112, which is protection against flash fires, not arc flash. Clothing can be dual-rated for compliance with ASTM F1506/NFPA 70E and NFPA 2112, but it has to state this on the label.
Unrated arc flash clothing and PPE present a very real threat to the well-being of the person wearing it. Those wearing it must not be allowed to work on or near any electrical power system or device that may be energized.
White is director of training for Shermco Industries in Irving, Texas. He can be reached at [email protected].
James White | Director of Training
James R. (Jim) White is the VP of Training Services at Shermco Industries, Inc., in Irving, Texas. He is a certified electrical safety compliance professional (CESCP) through the NFPA and one of approximately 130 Level IV senior certified technicians through NETA. A principal member for Shermco Industries on the NFPA Technical Committee “Recommended Practice for Electrical Equipment Maintenance” (NFPA 70B), he represents the interNational Electrical Testing Association (NETA) and is also an alternate member of NFPA Technical Committee “Standard for Electrical Safety in the Workplace” (NFPA 70E), a principal representative of NEC Code Making Panel CMP-13, and principal representative of ASTM F18 Committee “Electrical Protective Equipment For Workers.” White is a senior member of IEEE and past chairman (2008) of the IEEE Electrical Safety Workshop. In 2011, he received the IEEE/PCIC “Electrical Safety Excellence” award, and in 2013 he was honored with NETA’s “Outstanding Achievement Award.”
Chapter 9 of the NEC — Part 5