Discuss this Article 10
Anonymous (not verified)
on Feb 26, 2013
If a standard motor starter is utilized for the motor control, vs. a VFD, consider checking for proper coil voltage and proper contactor engagemnet strength. If correct, be sure to check for wear and burning on the contacts themselves. Do to normal arcing and wear contacts may become carboned and will limit proper voltage through the contact creating increased amperage.
on Feb 26, 2013
Voltage drop may be an issue. The load, cable size and the distance should be confirmed to calculate the voltage drop.The voltage drop may not be the root cause but can be a contributing cause.
on Feb 26, 2013
If you have access to a good thermal imager usit it to scan the electrical connections. We had a situation where we were blowing the fuses in the MCC for a motor but not blowing the smaller fuses in the local disconnect. We found that a loose connection in the MCC was causing the problem. Unce the connection was cleanes and tightened the problem went away.
on Feb 26, 2013
Verify the pressure is acurate you could be starting against a higher pressure in the recieving tank which could intermittently cause the fuses to blow. The pressure switch could be bad or out of calibration.
Tim (not verified)
on Feb 26, 2013
I'd check the following:
1 contactor(s), both if lead/lag used
2 compressor motor bearings
3 reservior tank backcheck valves (400 psi is hell of a head!)
Louconstant1 (not verified)
on Feb 26, 2013
You stated that you have 200hp motor, need more info, name plate,voltage, amps, hp, three phase? Letter? Etc. motor type, wire size? Then we can determine and come up with a solution. Using 2011 NEC -NFPA
Thanks louconstant
on Feb 26, 2013
call an electrician, lolzzz
on Feb 27, 2013
Based on the information already submitted I would also check the power factor and see if power factor correction is faulty or necessary. A 200HP motor is a large load to be starting across the line. I definitely would use a VFD or soft-start device for that large of motor regardless. If you have test equipment a power quality analyzer measuring the start up wave-shapes would provide valuable information as to the problem by indicating uniformity, voltage and current magnitude, angle, etc.
sparky Jr. (not verified)
on Feb 27, 2013
Allways increase the wire size For 200 H.P You should
go up to the next size that will solve your problem remember I squared X ressistence= less Heat!
on Mar 11, 2013
A lot of great suggestions. Sounds like possible Harmonic Currents. Testing with a True RMS Volt meter and Amp meter will tell the difference.