ECM Buyers' Guide
Illustrated Catastrophes
Nov 1, 2003 12:00 PM, By Joe Tedesco, NEC Columnist
A SHINING EXAMPLE OF POOR WORK
Not only is this installation missing an outdoor box required by 300.15, but it also uses an incorrect type of cable assembly for this particular location. Any luminaire (fixture) installed in a wet location must be installed so that water can't enter or accumulate in wiring compartments, lampholders, or other electrical parts. In addition, all luminaires installed in wet locations must be marked “Suitable for Wet Locations,” per 410.4(A), Luminaires (Fixtures) in Specific Locations, Wet and Damp Locations.
ONE SMELLY INSTALLATION
Are these service entrance cables truly protected? I don't think so. Where Type SE service cables are subject to physical damage, like in this driveway near the trash containers, they must be protected by one of the following:
  • Rigid metal conduit
  • Intermediate metal conduit
  • Schedule 80 rigid nonmetallic conduit
  • Electrical metallic tubing
  • Other approved means
See 230.50(A), Protection of Open Conductors and Cables Against Damage - Above Ground.
LAMPHOLDERS NOT ALLOWED
Certain types of listed luminaires (fixtures)may be installed in a clothes closet under specific conditions.Approved fixtures include surface-mounted or recessed incandescent luminaires with a completely enclosed lamp or surface-mounted or recessed fluorescent luminaires. Incandescent luminaires with open or partially enclosed lamps and pendant luminaires or lampholders may not be installed in a closet. See 410.8, Luminaires (Fixtures) in Clothes Closets.
WHERE'S THE COMPOUND?
A quick check of these explosionproof fittings revealed an improper installation. Per 501.5(C), sealing fittings must be listed for use with one or more specific compounds and must be accessible. Sealing compound must provide a seal against passage of gas or vapors through the seal fitting, and it can't be affect-ed by the surrounding atmosphere and liquids or have a melting point of less than 93°C (200°F). The minimum thickness of the sealing compound can't be less than the trade size of the sealing fitting and, in no case, less than 0.625 in.
It should also be noted that the cross-sectional area of the conductors permitted in a seal can't exceed 25% of the cross-sectional area of a rigid metal conduit of the same trade size unless it's specifically identified for a higher percentage of fill. And threaded joints must be made up with at least five threads fully engaged.
Found a Code violation? Send your photos to Joe Tedesco at 350 North St., Boston, MA 02113 or CodeViolations@JoeTedesco.com.
Acceptable Use Policy
what's wrong here?
Nov 5, 2009 11:50 AM
Oct 22, 2009 11:16 PM
Oct 8, 2009 3:32 PM
View all What's Wrong Here?
product of the week
Video camera scopes
November 16, 2009
Video camera scopes
Recent Comments
More...
Exterior Fixture Box for Brick or Stone
Installing a fixture box in a brick or stone wall just got easier with Arlington’s new adjustable depth box!
Gain years worth of insight in only 2-1/2 hours with Southwire’s 2009 Cable Innovation Road Show with Grounding Seminar. The agenda is packed with valuable information that focuses on installation tips!
Listen
Listen
resources
product info icon
product info
tradeshow icon
tradeshow
research icon
research
rss icon
rss
Browse Back Issues
Browse Back Issues
