CodeWatch Change Proposals
This is it. For the past four-and-a-half months CodeWatch has scoured the thousands of pages of proposals presented to the twenty Code-Making Panels to find those that could have the greatest effect on your work. We couldn't possibly cover them all, but those we did cover are presented here.
Code-Making Panel 2
Proposal 2-134a Sec. 210.12
It seems like everything associated with AFCIs has the potential to
stir up debate. Code-Making Panel 2 has proposed two significant
changes to the rules for arc-fault circuit interrupters, including new
text that specifies combination-type devices. The proposal was
accepted, but dissenting opinions presented by members of the panel
dispute the need for the change because although at least one
combination-type AFCI is UL Listed, it has yet to become commercially
available. It should be noted that as defined for this use,
"combination" refers to protection for parallel and series arcing, not
combined AFCI and GFCI protection.
Code-Making Panel 2
Proposal 2-211a, 210.52(C)(1)
The panel accepted a proposal to add the following exception:
"Receptacle outlets shall not be required on a wall directly behind a
range top or sink. The area directly behind a range top or sink is
determined as shown in Figure 210.52. Receptacle outlets in this
location shall not be considered as the required countertop
outlets."
Code-Making Panel 3
Proposal 3-26, Sec. 300.4(A)(2)
The panel accepted a proposal that clarifies that a nailer plate(s)
must protect the wiring method for its entire length where subject to
penetration. Otherwise, for example, where several cables are run
together through a header, a single plate may not be big enough to
protect all the cables. It also clarifies that you may need several
plates end-to-end if a cable runs parallel to a framing member without
the required 1.25-in. clearance.
Code-Making Panel 5
Proposal 5-37, Art. 250
The misuse of and confusion over the term "bonding" has grown so
troublesome that even a Code-Making Panel not responsible for its
application tried to do something about it. Although CMP-6 ultimately
deferred to CMP-5 on the issue of using "equipment bonding conductor"
in place of "equipment grounding conductor," CMP-5 accepted a proposal
to add the term "bonding" to the name of Art. 250. Four separate
proposals called for the change, which would acknowledge the fact that
there are just as many bonding requirements as grounding requirements
in the Article.
Code-Making Panel 5
Proposal 5-154 Sec. 250.64(B)
The problem with burying things underground is that sooner or later
someone is bound to dig them up. In the case of a buried conductor,
putting as much distance between the electricity it carries and an
errant shovel tip is one way to protect everyone involved in the
absence of conduit. Grounding electrode conductors may not typically
carry current, but that doesn't mean they don't need protection.
Despite suggestions that any depth requirements should be accompanied
by distance-from-building requirements, the panel accepted a proposed
additional paragraph to 250.64 that would require direct buried
grounding electrode conductors to be buried at least 12 in. below
grade. The proposal was brought about by the fact that few installers
and inspectors consider the burial requirements of Table 300.5 to be
applicable to grounding electrode conductors.
Code-Making Panel 6
Proposal 6-12 Sec. 310.6
The range of unshielded solid dielectric insulated conductors
acceptable for installation is shrinking considerably. Although 310.6
of the 2002 Code requires shielded conductors for voltages greater than
2,000V, an exception does provide for installations of unshielded cable
operating as high as 8,000V. However, this proposal would narrow that
exception to no more than 2,400V. Submitter David Brender of Copper
Development cites instances of arcing that could present safety
hazards. Despite garnering the necessary votes for acceptance, the
proposal may receive close scrutiny at the Code Panel meetings this
December, thanks to strong dissenting opinions that call for further
substantiation.
Code-Making Panel 7
Proposal 7-25, Sec. 322.10
It's typically easier to determine and govern the uses for which a
wiring method isn't acceptable. However, this Section tried to tackle
the uses for which flat cable assemblies are acceptable. The NEC
Technical Correlating Committee saw the problems inherent in keeping a
list of acceptable uses, and proposed deleting the Section altogether.
CMP 7 accepted the proposal, keeping only a list of uses for which flat
cable assemblies are not permitted (322.12).
Code-Making Panel 10
Proposal 10-39, Sec. 240.20(B)(1)(2)(3)
In another example of one word making all the difference, CMP-10
accepted the proposal to replace the word "approved" with "identified"
in reference to handle ties in 240.20. The current wording puts the
power to accept or reject a handle tie -- regardless of its intended
use -- in the hands of the Authority Having Jurisdiction. This change
would eliminate the subjective nature of the requirement and prevent
installers from using things like nails, screws, or wire as handle
ties.
Code-Making Panel 12
Proposal 12-33 Sec. 625.2
In response to the growing number of people who use golf carts or other
small 4-wheeled electric vehicles for short trips in and around golf
communities, CMP-12 has accepted a proposal to include "neighborhood
electric vehicles" to the definition of an electric vehicle in 625.2.
However, it should be noted that the new definition excludes golf carts
by name. Neighborhood electric vehicles, as defined by the Department
of Transportation, have a top speed of 25 mph and have automotive grade
headlights, seat belts, windshields, and brakes. It's important to
recognize that not all golf carts meet these requirements.
Code-Making Panel 14
Proposal 14-34 Sec. 501.15(B)(2)
Sometimes it's possible to have too much protection. Over time, the
requirement for sealing fittings in conduits that pass from Div. 2
locations into unclassified locations has come to mean different things
to different people. Despite the high cost and the fact that it's
unnecessary, it has become common to specify explosionproof seals.
However, in such instances the seal's only purpose is to minimize the
amount of gas or vapor within the Div. 2 location that can pass into
the unclassified area. The proposed change would add text that
explicitly states sealing fittings need not be explosionproof.
Proposals 14-29, 14-101, 14-105, etc.
Although 398.2 defines the term "open wiring on insulators" as an
exposed wiring method that uses cleats, knobs, tubes, and flexible
tubing for protecting and supporting single insulated conductors run in
or on buildings, there is no definition for the term "open wiring,"
which appears nine times throughout the Code. In each case it's used to
describe a cable that must have mechanical integrity and protection. A
set of proposals that would remove the undefined term from Chapters 5,
6, and 7 point out installations labeled this way are, in fact, not
open. A separate proposal was submitted for each instance.
Code-Making Panel 15
Proposal 15-18 Sec. 517.13(A)
Some people recommend changes to the Code based on anecdotal evidence
or experiences out in the field. Others, like George Straniero, AFC
Cable Systems, use fact-finding reports from nationally recognized test
agencies to prove their point. A March 2001 investigation conducted by
UL, which was also used to substantiate the amendment of 517-13(a)
Exception 1 in the 1999 Code, proves that the outer metal sheath of
Type MC cable that employs interlocked metal armor qualifies as an
acceptable ground return path in lengths not exceeding 100 ft, thus
meeting the requirements for branch circuits that serve patient care
areas. A proposed addition to the 2005 Code would require that the
cable be listed for the purpose, which would require specific cable
construction and performance requirements to maintain the acceptability
of the ground path. The fact-finding report found that when used in
combination with a grounding conductor, Type MC cable that employs
interlocked metal armor would cause a circuit breaker to open within 2
sec. The armor and grounding path also complied with the requirements
in UL 467, Standard for Grounding and Bonding Equipment, and it
couldn't be ignited under a high-impedance ground-fault current
test.
Code-Making Panel 16
Proposals 16-81 and 16-82, Sec. 800.6
The issue of "neat and workmanlike" installation practices has caused
plenty of debate in the electrical industry throughout the last few
years. The 2002 edition of the Code® was revised to delete a Fine
Print Note that directed users to several documents and standards that
defined "neat and workmanlike" installation of communications circuits
and equipment. In addition to a proposal put forth by James Brunssen of
Telecordia Technologies, Inc., that would clarify portions of the
Section, a second proposal would add back a revised version of the 1999
Fine Print Note that references ANSI/NECA/BICSI 568-2001, which defines
installation parameters.
Code-Making Panel 17
Proposal 17-6 Sec. 422.16(B)(4)
The items inside a vending machine aren't always good for you, but you
wouldn't expect the machine itself to be bad for your health. The U.S.
Consumer Product Safety Commission has investigated four electrocutions
caused by vending machine conductors faulting to the exposed frame of
the machine since 1995 -- a phenomenon that EC&M has covered
in a previous Forensic
Casebook column. In response, Bill King, the CPSC's chief engineer
for electrical and fire safety, submitted a proposal that would add a
new paragraph to Part IV of Art. 422 and require the use of
ground-fault circuit interrupters for cord-and-plug connected vending
machines.
Proposal 17-24 Sec. 422.31(B)
Performing maintenance on electrical equipment may require a lot of
thought, but keeping yourself safe while doing it shouldn't. With a
multitude of lockout devices available and uncertainty over whether
appliances will even provide a disconnect means other than a circuit
breaker, until now maintenance technicians have been responsible for
their own safety by coming prepared for almost any situation. If James
Dollard of IBEW Local 98 gets his way, though, that won't be the case
once the 2005 Code is published. His proposal would require that
regardless of what method is provided, the appliance must be
accompanied by a permanently installed lockout device on or at the
switch or circuit breaker used as the disconnecting means.
Code-Making Panel 18
Proposal 18-61 Sec. 410.15(B)
What do you do when you think it's OK to install something but you
don't have anything to tell you if you're doing it correctly? Despite
their widespread use and the fact that they provide as much protection
as their metal counterparts, nonmetallic poles made of concrete,
fiberglass, and PVC used to support luminaires have never been
specifically recognized by the Code as acceptable for use as raceway.
However, the Code doesn't specifically prohibit their use either. This
ambiguity has left installers of nonmetallic lighting poles with the
task of using an infrastructure component without ever knowing whether
they're doing it correctly. Any judgment calls were left up to the AHJ
or local inspector. A proposal before CMP 18 would eliminate references
to metal poles in 410.15(B), thereby broadening its scope to include
nonmetallic poles and clarifying the section's requirements.