Jul 1, 1999 12:00 PM, By Fred Hartwell, Senior Editor

Portable Standby Systems

Be careful when wiring standby systems from non-permanent sources. They don't fall under Art. 702, and a key safety rule in Art. 230 just disappeared.

As we approach the millennium, many homeowners who are convinced the power grid will fail on Jan. 1, 2000 are busy buying standby generators. If we're lucky, they'll approach qualified persons to make safe arrangements to use them. We hope the inspection community finds enough threads in this article to allow it to make enforcement decisions accordingly.

The EC&M panel's advice. Note the word "advice." The NEC, inadvertently in our view, turned dangerously deficient in the area of mandatory rules we've assumed for generations would prevent hazards to utility line crews. Therefore, this column departs somewhat from its format over the last nine years, where we always told you what the Code required on various issues. This month, we'll tell you what you should do.

Cord-connected generators. Most owners want to be able to move these generators around as they need them for other projects, instead of permanently wiring them. First, review the load. These are optional systems, so the owner decides what loads he wants connected. Size the cord per Sec. 445-5 to either 100% or 115% of rated generator output, and be sure you have overcurrent protection in the house accordingly (if it isn't in the generator), as covered in Sec. 445-4.

Then, avoid the temptation to put a plug on the end of this cord. You have to use a receptacle body, and wire the house connection with a flanged inlet to meet the new requirement for deenergized plug blades in Sec. 410-56(g).

In the house, connect the wire from the flanged inlet to the standby side of a manual transfer switch. Be sure that the switch is suitable for use as service equipment, as covered in Sec. 225-36. If you need to position the transfer switch remote from the point of entry, you'll need a switch near the point of entry that meets the same requirement.

Next, supply the transfer switch with a normal feeder from the house panel, sized and protected per Sec. 215-2(a) and Sec. 215-3. Wire from the transfer switch to a panel containing the circuits the owner wants, and which, per Art. 220, won't impose an overload on the standby system.

This arrangement meets the owners needs, and you can complete the work at a modest cost. Most importantly, your owner won't kill utility line crew personnel by inadvertently backfeeding the service conductors. In addition, with normal power on, you won't end up with energized blades in the flanged inlet.

What about Sec. 702-6? This section doesn't apply for two reasons. First, it doesn't actually require transfer equipment, only that, if installed, it should prevent inadvertent supply interconnections. Second, the scope of Art. 702 excludes portable equipment from coverage!

With Art. 702 out of the picture, what about Art. 230? With no transfer switch per se, the existing line up of circuit breakers and the feed from the flanged inlet become, collectively, the transfer equipment. Former Sec. 230-83, which referred to "transfer equipment, including transfer switches" (clearly suggesting coverage of other equipment than transfer switches) prohibited any possible interconnection of sources. We think interconnection is not only possible, but likely if you only rely on panelboard warnings to untrained owners.

Forgetting about the wider application of that rule, CMP 4 deleted Sec. 230-83 in the 1999 NEC, believing it to govern only the performance of transfer switches, a subject fully addressed in product standards. The 2002 Code should either reinstate Sec. 230-83, or broaden the scope of Art. 702, or both. Until then, inspectors need to apply more general rules, such as Sec. 110-2 requiring approval of all equipment.

Want to use this article? Click here for options!



Acceptable Use Policy
blog comments powered by Disqus

what's wrong here?

What's Wrong Here?

Nov 5, 2009 11:50 AM

What's Wrong Here?

Oct 22, 2009 11:16 PM

What's Wrong Here?

Oct 8, 2009 3:32 PM

View all What's Wrong Here?

product of the week

Video camera scopes

November 16, 2009

Video camera scopes

View all 2009 Products of the Week

Recent Comments

More...


EC&M TV

Exterior Fixture Box for Brick or Stone

Installing a fixture box in a brick or stone wall just got easier with Arlington’s new adjustable depth box!

Southwire's 2009 Cable Innovation Road Show

Gain years worth of insight in only 2-1/2 hours with Southwire’s 2009 Cable Innovation Road Show with Grounding Seminar. The agenda is packed with valuable information that focuses on installation tips!

Listen
Sizing Gen-Sets: Facts, Hints, and Good Judgment
Listen

The complexities of today’s commercial or industrial facility, with their equipment environment of linear and nonlinear loads, places a whole new light on sizing engine-generator sets.

Arc Mitigation - A Total System Approach
There’s no question the risk of arc flash hazards is real in the electrical industry. What many don’t always realize is the impact in business interruption from such events typically far outweighs the physical damage to equipment. View this On Demand Webinar!

Implementing an Industrial Ethernet Infrastructure that's Built to Last
This webinar explores the key benefits of implementing a robust complete, end-to-end Industrial Ethernet solution – from cabling and connectivity, to active components and associated hardware. View this On Demand Webinar!

resources

product info icon

product info

tradeshow icon

tradeshow

research icon

research

rss icon

rss

Browse Back Issues

Browse Back Issues