Code Forum

Dec 1, 1999 12:00 PM, By James Stallcup, Sr., and James Stallcup, Jr.

Learn the NEC rules on how to use the grounded neutral conductor as an equipment-grounding conductor.

Under certain conditions, you can ground all metal parts of enclosures used to install service equipment by the grounded neutral conductor on the supply side of the system. When you're using this type of grounding scheme, this includes the service weatherhead, service raceway, service meter base, and service equipment enclosure.

Using grounded neutral conductors on the supply side: Sec. 250 142(a)(1) through (a)(3). You can use the grounded neutral conductor as a current-carrying conductor and grounding means on the supply side of the service disconnecting means and supply side of a separately derived system as follows:

(1) On the supply side of service equipment disconnecting means.

(2) On the supply side of the main disconnecting means for separate buildings and structures, per Sec. 250-32(b).

(3) On the line side of the disconnect or overcurrent protection devices of a separately derived system per Sec. 250-30(a)(1).

Sizing grounded conductor for neutral current: Sec. 220-22. To control the maximum unbalanced load, you must compute the neutral load ampacity. Consider the neutral load (in amps) wherever you use a neutral in conjunction with one or more ungrounded phase conductors. On single-phase circuits using one ungrounded conductor and a neutral, the neutral will carry the same amount of current as the ungrounded phase conductor. However, since a two-wire circuit is rare, let's assume there is a neutral with two or more ungrounded phase conductors. If there are two ungrounded conductors using a shared neutral, the neutral must carry the total current in amps from both phase conductors; which is not an accepted practice.

Let's take a look at an example for clarification. Consider the ungrounded phase conductors supplying the main service panelboard in our example are 600kcmil THWN copper conductors (60 degreesC/75 degreesC terminals). You can determine the neutral conductor size by:

Step 1: Determine the load on each phase conductor. L1 = 112A, L2 = 110A, and L3 = 106A.

Step 2: Calculate the maximum unbalanced load. L1 = 112A.

Step 3: Select the proper size neutral conductor per Table 310-16. Here, 112A requires a No. 2 AWG conductor.

Sizing neutral to carry fault current: Sec. 250-24(b)(1) and (b)(2). When you ground an AC system (operating at less than 1000V), you must run the grounded neutral conductor to each service disconnecting means. The grounded neutral conductor size must not be less than requirements shown in Table 250-66. You must route this grounded neutral conductor with the phase conductors. If service conductors are larger than 1100kcmil (copper) or 1750kcmil (aluminum), you can't use Table 250-66. If the grounded conductor is larger than the above figures, the grounded neutral conductor size can't be smaller than 12.5% of the area of the largest phase conductor. If the conductors are paralleled, you must base the grounded neutral conductor size on the total circular mil area of the paralleled conductors per Sec. 250-24(b)(2) and Sec. 310-4.

Let's look at an example showing how to size an equipment-grounding conductor to clear ground-faults. The ungrounded phase conductors supplying the main service panelboard in our example are 600kcmil THWN copper conductors (60 degreesC/75 degreesC terminals). You determine the neutral conductor size by referring to Table 250-66. Here, No. 1/0 AWG THWN copper conductor was selected to meet Code.

Neutral tip. Sec. 310-15(b)(4)(c) requires you to increase the size of the neutral supplied by a 3-phase, 4-wire, wye-connected system if a major portion of the load consists of nonlinear loads saturated with harmonic currents. FPN 2 of Art. 220-Sec. 22 warns of this problem. Here, you may have to double the neutral in size or harmonic filters installed to correct the problem.

Want to use this article? Click here for options!



Acceptable Use Policy
blog comments powered by Disqus

what's wrong here?

What's Wrong Here?

Nov 5, 2009 11:50 AM

What's Wrong Here?

Oct 22, 2009 11:16 PM

What's Wrong Here?

Oct 8, 2009 3:32 PM

View all What's Wrong Here?

product of the week

Video camera scopes

November 16, 2009

Video camera scopes

View all 2009 Products of the Week

Recent Comments

More...


EC&M TV

Exterior Fixture Box for Brick or Stone

Installing a fixture box in a brick or stone wall just got easier with Arlington’s new adjustable depth box!

Southwire's 2009 Cable Innovation Road Show

Gain years worth of insight in only 2-1/2 hours with Southwire’s 2009 Cable Innovation Road Show with Grounding Seminar. The agenda is packed with valuable information that focuses on installation tips!

Listen
Sizing Gen-Sets: Facts, Hints, and Good Judgment
Listen

The complexities of today’s commercial or industrial facility, with their equipment environment of linear and nonlinear loads, places a whole new light on sizing engine-generator sets.

Arc Mitigation - A Total System Approach
There’s no question the risk of arc flash hazards is real in the electrical industry. What many don’t always realize is the impact in business interruption from such events typically far outweighs the physical damage to equipment. View this On Demand Webinar!

Implementing an Industrial Ethernet Infrastructure that's Built to Last
This webinar explores the key benefits of implementing a robust complete, end-to-end Industrial Ethernet solution – from cabling and connectivity, to active components and associated hardware. View this On Demand Webinar!

resources

product info icon

product info

tradeshow icon

tradeshow

research icon

research

rss icon

rss

Browse Back Issues

Browse Back Issues