ECM Buyers' Guide
Code Basics
Jun 1, 2000 12:00 PM, By James Stallcup, Sr. and James Stallcup, Jr.
Designing Electrical Systems for Fire Pumps
Since fire pumps are considered life safety equipment, they must be reliable.
When designing or installing electrical power supplies for fire pumps and their accessories, you must apply special rules as listed in (NFPA 70), the National Electrical Code (NEC), and the Standard for Centrifugal Fire Pumps (CFP) NFPA 20. These special rules protect the pump and associated electrical equipment from hazards that might cause complete failure due to floods, fire, high wind, etc. This article will review these rules and their application.
Power sources. Secs. 6-3.1 through 6-3.2.2 in NFPA 20 lists the requirements for the supply of electrical power to fire pumps and their accessories. Several sections in the 1999 NEC coordinate with NFPA 20 and reinforce those requirements. Let's take a look at each of these in more detail.
Service supply. The electrical service, whether supplied by the utility or the owner, must be reliable as well as located and installed to minimize the probability of damage by fire from within the premises [per CFP 20, 6-2.1, and NEC Sec. 695-3(a)(1)].
Where a second service is provided for the fire pump, as permitted in NEC Secs. 230-2(a)(1), 695-3(a)(1), and 695-6(b), you must route the service conductors outside of the building or encase them in at least 2 in. of concrete. If encased in concrete, the conductors are considered to be located outside the building. You can install the service conductors either overhead or underground.
Designers sometimes specify that an underground lateral supplies the fire pump system and an overhead drop or vice-versa supplies the service equipment.
Tap supply. If you use a tap to provide power to a fire pump, you're required to make the connection ahead of the main disconnecting means in the service equipment [per NEC Sec. 230-82(4)]. NEC Sec. 695-3(a)(1) does not allow you to make a tap for emergency systems in the same cabinet that houses service equipment containing the normal service. Designers usually specify that you install a tap ahead of the normal service equipment and place it in a completely different area or location.
CFP 20, Sec. 6-3.1 and Secs. 695-3(a)(1) and 695-6(a) allow you to route the conductors serving a fire pump and its accessories in a fire pump room without enclosing them in 2 in. of concrete if you protect them from possible damage by fire, structural failure, or operational accident.
Transformer supply. You shall install transformers installed to step up or step down the voltage serving a fire pump to comply with NEC Art. 450. Protect conductors from overcurrent in accordance with NEC Secs. 240-3, 240-100, and 240-101. The NEC requires overcurrent protection for transformers to meet the provisions of Table 450-3(a) or Table 450-3(b). Sec. 6-1 in NFPA 20 appears to refer to the NEC for the rules of installing transformers to supply power to fire pumps.
You can use a separate supply from a second transformer to supply power to a fire pump system. Therefore, if the main transformer supplying power to the normal service should for any reason fail, the second transformer would still energize the fire pump supply.
Generator supply. Sec. 6-6 in NFPA 20 allows on-site generators to furnish the power required to drive fire pumps. You should select these with sufficient capacity (kW) to permit the normal starting and running of the motors in the fire pump system -- plus all other connected loads. The installation of on-site generator systems shall comply with the requirements of Sec. 6-2.4.2 in NFPA 20 and NEC Sec. 695-3(b)(1).
Secs. 6-6.3 and 7-5.2.4 in NFPA 20 allow automatic sequencing of more than one fire pump to compensate for high inrush current due to starting and accelerating the load. For example, the fire pump motor with the greater inrush current per Table 6-5.1.1 starts first, the second largest starts second, and so on. After you start all fire pumps, you can connect other loads (if any) to the generator. Note: You must place transfer equipment in the pump room per Sec. 6-6.4 in NFPA 20.
On July 22, 1999 (to be effective 20 days thereafter), The National Fire Protection Association Standards Council issued a major interim revision to Sec. 695-3(b) of the NEC. This mandate makes it clear that you can connect a fire pump to a utility service. If this service is deemed unreliable, you can back it up with an on-site standby generator. Note: Such power sources must comply with the separation rules in NEC Sec. 695-3(b)(3).
Power wiring. Appendix A-6-2.3(3) in NFPA 20 and Sec. 695-6(b) of the NEC stipulate you must route the fire pumps feeder circuit conductors outside of the building, enclose them in 2 in. of concrete, or have a 1-hr fire resistance rating. Note that you must enclose wiring located in the pump room in rigid metal conduit, intermediate metal conduit, type MI cable, liquidtight flexible metal conduit, or liquidtight flexible nonmetallic conduit type LFNC-B per NEC Sec. 695-6(e).
You must compute feeder circuit conductors between the line of each power source no less than 125% times the sum of fire pumps and pressure maintenance motor(s), plus 100% of the associated fire pump accessory equipment. See NEC Secs. 695-6(c)(1) and (c)(2).
Overcurrent protection devices. If you install overcurrent protection devices ahead of the feeder pump circuits in the power supply for either utility or customer-owned supply systems, these protective devices shall be capable of carrying the locked-rotor current of the fire pump motor(s) and the pressure maintenance pump motor(s), and associated fire pump accessory equipment. See NEC Sec. 695-4(b)(1) and 695-5(b) for verification of this requirement.
When installed only in the feeder circuit to the fire pump and its accessories, NEC Secs. 230-90(a), Ex. 4 and 695-4(b)(1) require you to size the overcurrent protection device to carry the sum of the locked-rotor currents without opening.
The NEC permits you to locate a locked-rotor overcurrent protection device between the isolation means and fire pumps motor. If you install the overcurrent protection device in the fire pump controller as mentioned above, you must meet the following provisions: 1. The device shall comply with the following for a squirrel-cage or wound-rotor induction motor: a) Have a tripping time between 8 sec and 20 sec at locked-rotor current. (Note that this setting is about six times the full load current of a squirrel-cage motor.) b) The device shall be set at three times the motor's full load current. 2. For a DC motor, the device shall be set at four times the full load current of the motor, and the device has to be the instantaneous type.
Disconnecting means. You must provide disconnecting means to disconnect all plant circuits from the power supply source -- placing them in an accessible location in case of fire. The disconnecting means and overcurrent protection techniques must comply with NEC Art. 230, 240 and Sec. 695-4(b). In addition, the overcurrent protection device must meet the provisions of NEC Secs. 450-3 and 695-4(b)(1). Such protective devices are unique to fire pump loads.
The disconnecting means shall be capable of disconnecting the total locked-rotor current of the fire pump motor(s). Where the disconnecting means disconnects the fire pump motor(s), its accessories, and the plant loads, it shall be capable of disconnecting the sum of the locked-rotor current of such loads.
Controllers. All controllers you use in a fire pump system have to be suitable for use as service equipment per Sec. 7-1.2.4 in NFPA 20. You must install controllers as close as practical within sight of all motors in which they control. See Sec. 7-2.1 in NFPA 20 and Sec. 695-12(b) in the NEC.
You must install controllers at least 12 in. above the floor to protect them from water escaping from pumps or pump connections per Sec.7-2.2 in NFPA 20 and NEC Sec. 695-12(d).
You cannot use the fire pump controller as a junction box for wiring to supply other electrical equipment. You must not connect conductors supplying power for pressure maintenance (jockey or make up) pump(s) to the fire pump controller, per Sec. 7-3.4.4 in NFPA 20 and NEC Sec. 695-6(f).
Overcurrent protection devices shall not protect auxiliary control circuits that you use for the operation of the controller. See Sec. 7-3.5 in NFPA 20 for this requirement. Controllers in Sec. 7-1.2.2 in NFPA 20 are required to be sized to handle the driven load and selected to stand the available fault current for the circuit in which it is utilized.
Motors. Sec. 6-5.1.3 in NFPA 20 requires all motors used in the fire pump system to be rated for continuous duty. Motors have to be designed and selected to drive the pump load under all conditions of use without their full load amps being exceeded.
If you install motors at altitudes above 3300 ft, you must derate them according to altitude. For example, for every foot above 3300 ft the motor's full load rating in amps shall be derated by 1% for each 330 ft and 10% for each 1000 ft above 3300 ft. See CFP 6-5.2.2 in NFPA 20 and Part 14 to NEMA MG-1.
You must install the current-carrying parts of motors at least 12 in. above the finished floor for protection from water that may escape from the pumps.
Summary. After reviewing these requirements, it is obvious the designer must reference both the 1999 NEC (NFPA 70) and NFPA 20 to ensure a safe and reliable power source for supplying fire pumps.
Acceptable Use Policy
what's wrong here?
Nov 5, 2009 11:50 AM
Oct 22, 2009 11:16 PM
Oct 8, 2009 3:32 PM
View all What's Wrong Here?
product of the week
Video camera scopes
November 16, 2009
Video camera scopes
Recent Comments
More...
Exterior Fixture Box for Brick or Stone
Installing a fixture box in a brick or stone wall just got easier with Arlington’s new adjustable depth box!
Gain years worth of insight in only 2-1/2 hours with Southwire’s 2009 Cable Innovation Road Show with Grounding Seminar. The agenda is packed with valuable information that focuses on installation tips!
Listen
Listen
resources
product info icon
product info
tradeshow icon
tradeshow
research icon
research
rss icon
rss
Browse Back Issues
Browse Back Issues
