According to 312.6 of the 2002 NEC, what's the minimum wire bending space required in a 200A rated panelboard, at the main circuit breaker terminals, where the main circuit breaker is fed with 4/0 AWG THHN/THWN insulated conductors? The 4/0 AWG conductors are installed in parallel -- two per phase. The conductors enter the enclosure on the wall directly opposite the circuit breaker lugs, i.e., through the top of the enclosure, in-line with the circuit breaker terminals.
A) 5 inches
B) 6 inches
C) 7 inches
D) 7.5 inches
Answer: D
Explanation: Refer to 312.6(B)(2) and Table 312.6(B). Look in the Wire Size column; find 4/0 AWG. Look at the top heading in the column Wires Per Terminal - 2 (wires per terminal). The minimum distance required from the terminal of the circuit breaker to the wall of the enclosure opposite the circuit breaker lug is 7.5 inches. If the manufacturer hasn't provided the minimum 7.5 inches (which is unlikely), the electrical installer may have to bring the 4/0 AWG conductors into the enclosure through a sidewall, or the bottom of the enclosure, or some other point that isn't directly opposite the lugs of the circuit breaker.
Owen is the owner and president of National Code Seminars and the holder of master electrician certifications in 46 states.
Want to use this article? Click here for options!
Acceptable Use Policy
blog comments powered by Disqus
what's wrong here?
What's Wrong Here?
Feb 2, 2012 7:54 PM
What's Wrong Here?
Jan 19, 2012 4:06 PM
What's Wrong Here?
Jan 5, 2012 11:53 AM
View all What's Wrong Here?
product spotlight
Emergency lighting controls
Feb 9, 2012 8:40 AM
The UL924 emergency lighting control relay (ERC) mounts in the ceiling and features an automatic diagnostic feature ...
View all 2012 Product Spotlights
Free Product Info
Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.
Recent Comments
More...
Social Media
More ways to stay informed...
follow us on twitter
Find us on Facebook
EC&M TV
Arlington CP9000
Arlington's new 9" diameter ceiling cover plate is the neatest way to cover unused "high hat" cans. With no tools needed, installation couldn't be faster!...
Arlington Gangable Boxes
Designed for new or retrofit applications, these snap-together gangable plastic boxes eliminate the need to construct a multiple-gang steel box out of several individual ones...
Understanding NEC Requirements for Solar Photovoltaic Systems
During this session, Mike Holt will address possible conflicts or confusing NEC requirements, provide tips on proper electrical installation techniques, and discuss the dangers related to improper installations. View this On Demand Webinar!
resources
product info icon
product info
tradeshow icon
tradeshow
research icon
research
industry links
industry links
rss icon
rss
Browse Back Issues
Browse Back Issues