Q. I’m working on an electric gate installation. Can I install control wiring in the same raceway with electrical power conductors?
A. Maybe. According to 725.26(B)(1), Class 1 circuits can be placed in the same cable, enclosure, or raceway with power-supply circuits, if the equipment powered is functionally associated with the Class 1 circuit (Figure 725-26B1 UN725-25). However, 725.55(A) states that Class 2 and Class 3 circuit conductors must not be placed in any enclosure, raceway, or cable with conductors of electric light and power. How do you know if you have a Class 1 or Class 2 circuit? Check with the manufacture and find out if the control circuit power supply is intended for Class 2 or Class 3 wiring.
Keep in mind that Exception 2 of 725.52(A) allows you to reclassify a Class 2 or Class 3 circuit into a Class 1 circuit if the Class 2 or Class 3 equipment markings required by 725.42 are eliminated and the entire circuit is installed in a Chapter 3 wiring method [725.55(D)(2)(b)] and 600V conductors are used. Note that Class 2 and Class 3 circuits reclassified and installed as Class 1 circuits are no longer Class 2 or Class 3, regardless of the continued connection to a Class 2 or Class 3 power source.
Got a question for Mike? E-mail him at mike@mikeholt.com.
Want to use this article? Click here for options!
© 2012 Penton Business Media, Inc.
Latest Articles
Thermal imaging camera
Feb 3, 2012 8:45 AM
Takeoff/estimating software
Feb 2, 2012 9:08 AM
Generator sizing software
Feb 1, 2012 7:28 AM
Trending Articles
Acceptable Use Policy blog comments powered by Disqus
advertisement
product spotlight
Feb 3, 2012 8:45 AM
The Heat Spy is a high-speed, 30-Hz, 160 × 120 pixel thermal imaging camera...
View all 2012 Product Spotlights
Free Product Info
Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.