Q. Can a single transfer switch be used to supply both emergency and non-emergency loads, such as a UPS for telecom equipment?
A. No, a single transfer switch is not permitted to serve emergency and non-emergency loads [700.6(D)]. However, a single generator is permitted to serve emergency and non-emergency loads, provided multiple transfer switches are used, and automatic load shedding ensures adequate power for the emergency loads [700.5(B)] (Figure below).
The building feeder disconnecting means is permitted to be locked closed if there is concern that the opening of the readily accessible disconnect could result in a hazard to persons or property, lets say because of vandals or terrorism.
Got a Code question for Mike? Send it to him at mike@mikeholt.com.
Acceptable Use Policy
blog comments powered by Disqus
Want to use this article? Click here for options!
product of the week
Work gear
January 5, 2009 10:53 AM
DeWalt Work Gear
View all 2009 Products of the Week
Recent Comments
Follow comments on ecmweb.com
Arc Flash Conferences   Code Change Conferences
Professionals provide answers to your questions.
Do you have any technical paper explaining IBC?
iGard Resistance Grounding Q&A BookletDownload the Resistance Grounding Q&A Booklet
I-Gard
EC&M TV
Retrofit 2-Gang TV Box(TM)
Arlington’s recessed two-gang TV BOX™ for old work allows you to mount LCD and plasma TVs, and other system components flush against the wall.
Listen
"Sizing Gen-Sets: Facts, Hints, and Good Judgment"
Listen
Sponsored By:
resources
product info icon
product info
tradeshow icon
tradeshow
research icon
research
rss icon
rss
Back to Top
Browse Back Issues
Browse Back Issues