Code Q&A
Q. How would you size the bonding wire to a motor that’s protected by an inverse time circuit breaker?
A. The equipment grounding (bonding) conductor must be sized in accordance with Table 250.122, based on the ampere rating of the circuit-protection device, but in no case is it required to be larger than the circuit conductors.
For example, a 5-hp, 208V, 3-phase motor with an FLC of 16.7A, and that’s wired with 12 AWG [430.22(A)], with a 40A short-circuit, ground-fault protection device [430.52(C)(1)] would have a 12 AWG equipment grounding (bonding) conductor. Since the circuit wires are 12 AWG, there is no reason to install a 10 AWG equipment grounding (bonding) conductor. Please review requirement in 250.122, which in part states "equipment grounding conductors shall not be smaller than shown in Table 250.122 but shall not be required to be larger than the circuit conductors supplying the equipment."
Got a question for Mike? E-mail him at mike@mikeholt.com.
Want to use this article? Click here for options!
© 2012 Penton Business Media, Inc.
Latest Articles
Thermal imaging camera
Feb 3, 2012 8:45 AM
Takeoff/estimating software
Feb 2, 2012 9:08 AM
Generator sizing software
Feb 1, 2012 7:28 AM
Trending Articles
Acceptable Use Policy blog comments powered by Disqus
advertisement
product spotlight
Feb 3, 2012 8:45 AM
The Heat Spy is a high-speed, 30-Hz, 160 × 120 pixel thermal imaging camera...
View all 2012 Product Spotlights
Free Product Info
Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.