Code Q&A
Q. Is a 125V duplex receptacle required to be rated 20A, when placed on a 20A circuit? A. The Code permits a 15A, 125V duplex receptacle on a 20A multioutlet branch circuit [210.21(B)(3)]. Primarily, because the maximum cord-connected load that can be placed on each 15A receptacle, is 12A in accordance with the plug configuration [210.21(B)(2)]. Still confused by the Code? Send your questions to Mike.
Q. Is it a violation of the Code to protect temporary lighting circuits with a GFCI? I’ve seen exposed temporary lighting wire (wire nuts fell off or were missing) touching metal studs, thereby presenting a potentially deadly work environment.
A. The NEC is silent on this issue, so this means it’s okay to GFCI-protect temporary lighting circuit conductors. However, to prevent a construction site from being placed in the dark by a ground fault, temporary lighting shall not be installed on the branch circuit that supplies receptacles [527.4(D)].
Note: Receptacles rated 15A or 20A, 125V used to supply temporary power for construction, remodeling, maintenance, repair, or demolition of buildings, structures, equipment, or similar activities shall be GFCI protected [527.6].