ESS

Top Changes in the 2023 NEC for Energy Storage Systems

Feb. 15, 2024
Why even the smallest modifications in the Code can be relevant to your system design

Whether you are an industry veteran or a DIYer out over your skis, you’ll have to grapple with the National Electrical Code (NEC) if you want to install an energy storage system (ESS). More specifically, you’ll have to grapple (metaphorically, of course) with your local electrical inspector. In the world of solar and battery storage, the NEC is king — and it’s what your inspector will be thinking about when you’re closing out your construction permits.

Since 1897, the good folks at the National Fire Protection Association (NFPA) have been helping keep you and your neighbors safe by making the rules for properly designing and installing electrical systems. As technology advances and industry workers identify and find solutions to new problems, the Code itself gets updated. This happens every three years, and 2023 marked the latest revision to the NEC. While only some jurisdictions have adopted the 2023 version as of this writing, it will be adopted by other states and jurisdictions over time.

Much of the Code remains unchanged from cycle to cycle, so why take the time to peruse the new version of the NEC? Missing seemingly small modifications relevant to your system design can make the difference between a smooth-sailing install and one caught up in a permitting logjam. In addition, inspectors are, while admirable in their service, subject to the same human flaws as you and me. If you spend time studying the latest version of NEC, you might find you can clear up otherwise costly misunderstandings on inspection day with a simple conversation.

Mayfield Renewables recently spoke with members of the NFPA Code Making Panel involved in developing the 2023 NEC to help clarify and illuminate ESS-related changes in Art. 706. Let’s walk through them one by one.

Section 706.1 — Scope and Relocation of Definitions

The first notable change is around definitions, which, in prior versions of the NEC, were scattered throughout various Articles. Definitions are now aggregated into Art. 100. Looking up a term (from anywhere in the NEC) just got much more straightforward.

The scope of Art. 706 states: “This article applies to all energy storage systems having a capacity greater than 3.6 MJ (1 kWh) that may be stand-alone or interactive with other electric power production sources. These systems are primarily intended to store and provide energy during normal operating conditions.”

The 2023 NEC now includes a new Informational Note that clarifies what types of ESSs require compliance with Art. 706. Informational Note No. 1 states: “See Art. 480 for installations that meet the definition of stationary standby batteries.”

Article 480 was developed before Art. 706, and this note clarifies that certain types of systems apply to one or the other. Article 706 applies to the vast majority of ESS installed nowadays. The “stationary standby batteries” referenced in the note indicate that Art. 480 applies to legacy-type systems designed purely for backup power. Stationary standby batteries are programmed exclusively for resilience and do not cycle during normal operation. Except during charging, they should not interact with the grid, a generator, or even PV equipment. For ESSs that are not stationary standby systems, Art. 706 applies.

Section 706.15(A) — ESS Disconnecting Means

Disconnects are basically big switches that can be flipped by a technician, utility worker, or firefighter to turn off all or part of an electrical system. A typical ESS will have one or more disconnect switches, with additional disconnects to isolate the PV portion of a system. This usually includes disconnects in the DC and AC portions of the circuitry.

Section 706.15, which is not new in 2023, describes the special requirements for ESS disconnecting means, which are in excess of other disconnects found in the system. Importantly, the language of Sec. 706.15(A) has been cleaned up to make clear that these special requirements apply only to the ESS disconnecting means.

“Means shall be provided to disconnect the ESS from all wiring systems, including other power systems, utilization equipment, and its associated premises wiring.”

This is a welcome change because many inspectors have previously misinterpreted the requirements of Sec. 706.15 to apply to all disconnects in the system. Since this is a clarification and not a change of substance, you may be able to work with a benevolent inspector to avoid misunderstandings and the burden they create — even when the jurisdiction has not adopted the NEC.

Section 706.15(B) — ESS Disconnecting Means Requirements

What are these special requirements for the ESS disconnecting means? There are several. One updated requirement is related to location and control.

“The disconnecting means shall be readily accessible and shall comply with one or more of the following:

“1) Located within the ESS

“2) Located within sight and within 3 m (10 ft) from the ESS

“3) Where not located within sight of the ESS, the disconnecting means, or the enclosure providing access to the disconnecting means, shall be capable of being locked per Sec. 110.25.”

These rules exist to protect technicians working on the ESS by ensuring it does not become energized without their knowledge. Note that the ESS disconnecting means must meet only one of these conditions. The first applies to an ESS that is packaged within a single unit and contains an integrated disconnecting means, which can be the simplest solution for the designer if it’s an available option. Disconnects not within sight and within 10 ft of the ESS must also be lockable per Sec. 110.25.

Section 706.15(B) — ESS Emergency Shutdown Function

Section 706.15(B) also contains language that has been relocated and modified, which relates to a required “emergency shutdown function” of the ESS in one- and two-family dwellings.

“For one- and two-family dwellings, an ESS shall include an emergency shutdown function to cease the export of power from the ESS to the premises wiring of other systems. An initiation device(s) shall be located at a readily accessible location outside the building and shall plainly indicate whether in the ‘off’ or ‘on’ position. The ‘off’ position of the device(s) shall perform the ESS emergency shutdown function.”

Crucially, this does not describe a disconnect, but only a shutdown initiation function device. Therefore, the system does not need to send an energized circuit from the ESS location outside the building. Instead, this function can be accomplished with a switch that sends a control signal to a device within the ESS that can initiate the emergency shutdown.

Unlike the disconnect itself, that switch does not need to be lockable. This is not a rapid shutdown function, so don’t confuse these two things. However, it may be possible for the industry to provide methods of combining the ESS emergency shutdown function with PV rapid shutdown. Finally, in cases where the ESS disconnecting means is incorporated into the ESS system itself (e.g., an ESS with an integrated inverter), the device manufacturer may provide a means of operating it with a control circuit.

Section 706.15(E) — Disconnecting Means for Batteries

In case you haven’t had enough of disconnecting means, the 2023 NEC also has new requirements for such means in an ESS where the batteries are separate from the ESS electronics and are subject to field servicing.

As per Sec. 706.15(E), “In cases where the battery is separate from the ESS electronics and is subject to field servicing, 706.15(E)(1) through (E)(4) shall apply.

“1) A disconnecting means shall be provided for all underground conductors. A disconnecting means shall be readily accessible and located within sight of the battery.

“2) Battery circuits exceeding 240VDC nominal between conductors or to ground shall have provisions to disconnect the series-connected strings into segments not exceeding 240VDC nominal for maintenance by qualified persons. Non-load-break bolted or plug-in disconnects shall be permitted.

“3) Where a disconnecting means is provided with remote controls to activate the disconnecting means and the controls for the disconnecting means are not located within sight of the battery, the disconnecting means shall be capable of being locked in the open position, in accordance with Sec. 110.25, and the location of the controls shall be field marked on the disconnecting means.

“4) The disconnecting means shall be legibly marked in the field. The marking shall be of sufficient durability to withstand the environment involved and shall include the following:

“1) Nominal battery voltage

“2)  Available fault current derived from the stationary standby battery system

“3) An arc-flash label in accordance with acceptable industry practice

“4) Date the calculation was performed.”

While this may appear to add a significant burden to ESS design, note that these requirements only apply when the batteries are both separate from the ESS electronics and require field servicing. These rules are there to protect technicians and the sites where they are installed in cases where they apply.

About the Author

Ryan Mayfield

Ryan Mayfield discovered his passion for renewable energy early in his college career at Humboldt State while pursuing his degree in Environmental Resources Engineering. Ryan was exposed to the exciting possibilities of solar power and his desire to learn more and be involved in the solar industry only grew as he continued his studies. Once he got his hands on an actual PV installation during a class with Solar Energy International, Ryan knew exactly how he wanted to spend his working days. Early in his career he worked as an installer, provided technical support for a renewable energy retailer, and moved up to Engineering Manager at a national renewable energy wholesale distributor.

Ryan has been working in the renewable energy field since 1999 and founded Mayfield Renewables in 2007. His career has blended technical expertise with an affinity for technical writing and education. While serving as CEO at Mayfield Renewables, Ryan was also the PV Systems Technical Editor for SolarPro Magazine from 2010 to 2018, where he regularly wrote feature articles and was a regular contributor to Home Power magazine. He is also the author of PV Design and Installation for Dummies (published in 2010) and teaches nationwide PV courses on topics such as: National Electrical Code, Oregon Solar Code and PV systems, commercial PV systems, and PV + Storage. Ryan holds a Limited Renewable Energy Technician (LRT) license in Oregon.

Ryan lives in Corvallis, Oregon with his wife, three children, and one dog. He enjoys spending quality time with his family, competing in triathlons, traveling, and a good scotch. 

Voice your opinion!

To join the conversation, and become an exclusive member of EC&M, create an account today!

Sponsored Recommendations

8 Types of Electrical Conduit and Their Uses

Electrical conduit is a tube or raceway used to house and protect electrical wires within a building or structure. From data centers to underground subways to ports and bridges...

How to Calculate Labor Costs

Most important to accurately estimating labor costs is knowing the approximate hours required for project completion. Learn how to calculate electrical labor cost.

A Powerful Duo: Fiberglass conduit and solar applications

Learn how strong, durable fiberglass conduit excelled in an environment with dense cable and helped make a complex burial much simpler for the contractor to help this customer...

Champion Fiberglass® Conduit Protects Cabling For New York's First Offshore Wind Farm

Learn how fiberglass conduit supported a heavy cable load and a buried installation to help this project reach a successful outcome.