NEC in the Facility
Retrofits, upgrades, and additions can result in a change to the "total load" used for sizing service conductors. Don't look only at the size of your service transformer(s) when adding equipment, upgrading HVAC, or making other configuration changes. Service conductors that were correctly sized with load diversification and other mitigating factors may suddenly be undersized.
Any time you add or change a load, you should recalculate the required ampacities of the conductors for the branch circuit, feeder, and service supplying that load. The service is the most critical, as loss of those conductors will shut down the whole area supplied by that service.
The ampacity of service conductors before any adjustment or correction factors must be at least the sum of the noncontinuous loads plus 125% of the continuous loads [230.42]. But if the service-entrance conductors terminate in an overcurrent protection device (and its assembly) listed for operation at 100% of rating, use the sum of noncontinuous and continuous loads.
Calculate each load per Art. 220, Part III, IV, or V as appropriate. Determine ampacity per 310.15.
Want to use this article? Click here for options!
© 2012 Penton Business Media, Inc.
Latest Articles
Annunciator Card Redesign Helps Modernize California Water Department
Feb 8, 2012 11:57 AM
Toroidal power transformers
Feb 8, 2012 8:39 AM
Modular controllers
Feb 7, 2012 8:47 AM
Trending Articles
Acceptable Use Policy blog comments powered by Disqus
advertisement
product spotlight
Feb 8, 2012 8:39 AM
These toroidal power transformers are designed for medical applications...
View all 2012 Product Spotlights
Free Product Info
Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.