Your facility has a small IT room that contains its servers. Each server rack receives power through its own rack-mounted UPS. The UPS event logs show frequent voltage spikes and repeated bouts of high THD (total harmonic disturbance). This room is on its own power transformer and panel (a separate transformer/panel supplies the lights). The receptacles are all isolated ground.
Using a UPS as a crutch instead of as insurance is tempting fate. You need to solve this problem before a UPS gets cooked. Where are the spikes and high THD coming from?
Your first clue is the use of isolated ground. The concept of "isolated ground" is actually referring to deferred bonding. It really has nothing to do with grounding (see NEC Art. 100 definitions). Essentially, you're insulating things so that you connect the supply end of the bonding jumper at a point near the source rather than the load (see IEEE Standard 142).
The typical IG installation is incorrect, adding problems that weren't there without it. In most cases where an IG is implemented:
  • It's done instead of meeting the basic requirements provided in IEEE Standard 142.
  • It doesn't solve any problems, even if implemented correctly.
  • It's implemented in a way that allows potential to exist between metallic objects.
This last item is probably the underlying problem here. If you're seeing spikes on the UPS event logs and those UPSs are supplied by IGs, suspect bonding errors in the IG implementation. Refer to IEEE Standard 142 for correct implementation, or forego the IG altogether. Though the UPSs have protected your servers thus far, they aren't intended to bandage errors that violate applicable codes and standards. Your current situation may nullify your UPS warranty.
The spikes may be originating outside the room. Use a power analyzer on the supply side of the transformer to see what you're dealing with.
"Dirty power" may be coming from inside that room — whether also coming from outside or not. Look at the other loads on that panel. Typically, where there are computers there are also printers and scanners. Does the room have a laser printer? If so, run power from a different panel just for this kind of noisy load.
MRO Insider
Safety
Mar 9, 2010 12:46 PM
The best protection against arc blast is "don’t be there." This, however, isn't always possible. The next best precaution is...
NEC in the Facility
Mar 9, 2010 12:43 PM
Most facilities today have surge arresters on the building supply (service). These are typically bought on a budget mentality that results in a waste of the entire investment. It doesn't have to be that way...
Failed Repairs
Mar 9, 2010 12:42 PM
A repair that isn't done correctly is a failure waiting to happen. Some common errors include...
Mar 9, 2010 12:27 PM
A rash of motor failures has afflicted your plant. Your plant engineer read some application notes from the Web site of a test instrument manufacturer and subsequently used a power analyzer on the feeders of these motors...
Acceptable Use Policy
what's wrong here?
Whats Wrong Here?
Mar 11, 2010 12:54 PM
Feb 18, 2010 5:04 PM
Feb 4, 2010 5:06 PM
View all What's Wrong Here?
product of the week
CAD Software
March 15, 2010
CAD Software
View all 2010 Products of the Week
Shocking Stats
54
More Industry Statistics
Recent Comments
More...
Professionals provide answers to your questions. Become an expert!
Arlington CED1 Entrance Hoods
The Scoop Series CED Entrance Plates and Hoods are reversible, non-metallic, single and two-gang versions...
Gain years worth of insight with Southwire’s 2009 Cable Innovation Road Show with Grounding Seminar!
George Brown College
Online Tech Training – Electronics, PLC, and Robotics programs at George Brown College.
Listen
Listen
resources
product info icon
product info
tradeshow icon
tradeshow
research icon
research
rss icon
rss
Browse Back Issues
Browse Back Issues