© Christian Delbert | Dreamstime.com
HVAC Equipment
NEC: Air Conditioning and Refrigerating Equipment — Part 6
June 1, 2023
A review of Art. 440, Part VI requirements
Article 440, Part VI provides the requirements for motor-compressor and branch-circuit overload protection. Application and selection [440.52] is broken down into protection of the motor-compressor [440.52(A)] and protection of motor-compressor control apparatus and branch-circuit conductors [440.52(B)].
To protect the motor-compressor, you have four choices. The text for each one is longish, but to summarize:
  1. Separate overload relay.
  2. Integral thermal protector.
  3. Fuse or inverse time circuit breaker.
  4. Protective system.
To protect the motor-compressor control apparatus and branch-circuit conductors, you also have four choices. And they are almost identical to the ones for protecting the motor.
If you use an overload relay or other device for motor overload protection and it isn’t capable of opening short circuits, you must protect it with fuses or inverse time circuit breakers [440.53].
Motor compressors and equipment on a 15A or 20A 120V circuit, or 15A 208V or 240V circuit:
  • If not cord and plug connected, must have both overload protection [440.54(A)] and sufficient time delay to permit starting [440.54(B)].
  • If cord and plug connected, must have overload protection [440.55(A)] and sufficient time delay to permit starting [440.54(C)]. Also, the rating of the plug and receptacle or cord connector must not exceed 20A and 125V or 15A at 250V [440.44(B)].