© Wiroje Pathi | Dreamstime.com
Industrial Chiller Motor Maintenance
NEC: Air Conditioning and Refrigerating Equipment — Part 5
March 3, 2023
Article 440, Part V provides the requirements for the motor controllers used in HVAC and refrigeration compressors.
Article 440, Part V provides the requirements for the motor controllers used in HVAC and refrigeration compressors. The text is dense, so let’s break it down.
Every motor-compressor controller must have two ratings [440.41(A)], and these are based on the compressor.
  1. Continuous-duty full-load current rating. Its value must be must be at least that of the nameplate-rated load current or the branch-circuit selection current (whichever is the greater of the two) of the compressor.
  2. Locked-rotor current rating. Its value must be at least that of the locked-rotor current of the compressor.
But what if the motor controller is rated in horsepower and doesn’t have one of these ratings? Then you must determine the equivalent currents from one of these tables:
  1. Equivalent full-load current rating, use Table 430.248, 249, or 250 as applicable. 248 applies to single-phase motors, 249 applies to two-phase motors, and 250 applies to three-phase motors.
  2. Locked-rotor current rating, use Table 430.251(A) or (B) as applicable. (A) applies to single-phase motors, use (B) for two- and three-phase motors of Design B, C, or D.
What if a controller serves more than one load? Then determine the combined load per 440.12(B). The number you come up with is the minimum vale for the continuous-duty full-load current rating and the locked-rotor current rating of that controller [440.41(B)].
The requirements for rating motor controllers not in hermetic motor circuits are in Article 430, Part VII. A key difference is instead of requiring the ratings to be at least as big as the compressor rating, Article 430 requires the rating to be at least as big as the motor rating.