Oko_SwanOmurphy/iStock/Thinkstock
Staying Safe with Temporary Light and Power
March 5, 2019
If temporary power means bringing service to the site, you must apply the requirements of Art. 230.
While it’s true the requirements for temporary wiring in the National Electrical Code (NEC) [Art. 590] are “relaxed” compared to those of permanent wiring, it’s not true that temporary means “slap it up” in any convenient manner.  For example, if it involves a service (bringing power to the site) you must apply the requirements in Art. 230.
Here are some highlights from this part of the NEC:
  • Since we don’t run temporary cables and cords in raceway, you must provide adequate support [Sec. 590.4(J)] and protection [Sec. 590.4(H). For example, route them out of the way of foot traffic, avoiding sharp edges.
  • If you use lamps, they must be protected from accidental contact or breakage by a suitable luminaire or lampholder with a guard [Sec. 590.4(F)].
  • You must protect personnel with GFCIs [Sec. 590.6]. But test them during and after installation. The protection provided by GFCIs is often bypassed due to incorrect wiring. Use a meter to verify the supply wires are, indeed, the supply wires and the wires connected on the load side are not supply wires.