Quizzes on the Code

Choose the best answer:

1. What size nonfused disconnect are you required to install for an air-conditioning unit with a compressor rated at 29A and a condenser rated at 2.5A?

(a) 20A (b) 30A (c) 60A (d) 100A

2. What size horsepower-rated disconnect are you required to install for an air-conditioning unit with a compressor rated at 29A and a condenser rated at 2.5A with a locked-rotor current rating (LRA) of 180A? (Note that the supply is 480V, 3-phase.)

(a) 25 hp (b) 30 hp (c) 40 hp (d) 50 hp

3. What size horsepower-rated disconnect are you required to install for the following loads on a 3-phase, 230V system?

• A/C unit with a compressor rated at 29A with a 200A LRA

• A/C unit with a compressor rated at 24A with a 150A LRA

• A/C unit with a compressor rated at 20A with a 140A LRA

(a) 20 hp

(b) 30 hp

(c) 35 hp

(d) 40 hp

4. What size disconnecting means (in horsepower) is required to disconnect the following loads on a 3-phase, 230V system?

• Motor rated at 38A with a 212A LRA

• A/C unit with a compressor rated at 28A with a 160A LRA

• A/C unit with a compressor rated at 24A with a 160A LRA

(a) 15 hp

(b) 20 hp

(c) 30 hp

(d) 35 hp

5. A cord-and-plug device may serve as the disconnecting means for a room air conditioner if it operates at:

(a) 120V or less

(b) 150V or less

(c) 250V or less

(d) 300V or less

Answers and Discussion:

1. (c), 60A. You must size the disconnect based on the full-load current rating of the nameplate or the nameplate branch-circuit selection current of the compressor, whichever is greater. The multiplier is 115%.

[29A + 2.5A] × 115 = 436.2A

36.2A requires a 60A disconnect

Stallcup’s Code Loop: Secs. 440-12(a)(1) and 240-6(a).

2. (a), 25 hp. When working with nameplate amperage ratings or branch-circuit current ratings instead of horsepower ratings, you must select the horsepower amperage rating from Tables 430-147 through 430-150. If the nameplate fails to list the LRA rating of the motor, you must select the horsepower amperage rating from Tables 430-151(A) and (B).

31.5 FLA requires 25 hp

180 LRA requires 25 hp

Stallcup’s Code Loop: Sec. 440-12(a)(2), Tables 430-150 and 430-151(B).

3. (c), 35 hp. Same explanation as in answer 2.

The disconnecting means must be rated at 35 hp.

Stallcup’s Code Loop: Sec. 440-12(b), Tables 430-150 and 430-151(B).

4. (d), 35 hp. When working with two or more hermetic motors or combination loads (such as hermetic motor loads, standard motor loads, and other loads), you must separate your totals to determine the rating of a single disconnecting means.

Therefore, the disconnecting means is required to be rated at 35 hp.

Stallcup’s Code Loop: Sec. 440-12(b)(2), Tables 430-150 and 430-151(B).

5. (c), 250V or less. A cord-and-plug device may serve as the disconnecting means for a room air conditioner if it operates at 250V or less, its controls are manually operated, it’s located within 6 ft of the floor, and it’s accessible to the user.


Want to use this article? Click here for options!





Acceptable Use Policy
blog comments powered by Disqus

what's wrong here?

What's Wrong Here?

May 10, 2012 12:44 PM

What's Wrong Here?

Apr 19, 2012 10:09 AM

What's Wrong Here?

Apr 5, 2012 2:27 PM

View all What's Wrong Here?

product spotlight

EV charger tester

May 25, 2012 8:26 AM

EV charger tester

The Electrician is portable tester that verifies critical power and safety requirements of electric vehicle (EV) chargers...

View all 2012 Product Spotlights

Free Product Info

Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.

Recent Comments

More...


Social Media

More ways to stay informed...

follow us on twitter

Find us on Facebook

EC&M Whitepaper

Arc Mitigation –A Three-Step Approach

Did you know that an arc-flash incident hospitalizes 5-7 workers per day in North America, severely impacting processes and profitability with lost production? Download This Sponsored Whitepaper Today!

What's New in Residential Cabling?
Date: Wednesday, May 30, 2012
Time: 2:00pm ET


In this The Home Depot sponsored Low Voltage Webinar, Ron Kipper RCDD / NTS will discuss the need for compression style coaxial connectors and the migration of the entire CATV, Satellite and Audio / Video industry to them. Register Today!

Grounding Versus Bonding
Now Available On-Demand


In this 60-minute FREE webinar, Mike Holt of Mike Holt Enterprises, Inc. will explain the purpose of grounding and bonding as related to the most current requirements set forth in the 2011 NEC. Register to View On-Demand!

resources

product info icon

product info

tradeshow icon

tradeshow

research icon

research

industry links

industry links

rss icon

rss

Browse Back Issues

Browse Back Issues