It Pays to Find the Right Solution

As the facilities manager for Reuters America, New York, John Lasher constantly evaluates the safety, reliability, and efficiency of the facility's electrical systems. Most of the load is nonlinear and consists of components such as computers and work stations.

Lasher discovered high amounts of harmonic current on two subsystems fed by 300kVA transformers. The current was especially high in the neutrals. He was not surprised to find the majority of this current — 250A in one case — was at the third harmonic. Infrared testing of the transformers confirmed both were operating in excess of their temperature class ratings.

Lasher and others at Reuters considered several ways to reduce harmonic risk to the facility, including doubling neutral wires and replacing transformers with k-rated units. Ultimately, they decided to install SysteMax on the secondary side of both transformers.

SysteMax is a harmonic suppression system from Harmonics Limited, Monroe, Conn. Connected at the transformer, the system prevents the flow of third-harmonic current — thereby eliminating the need to beef up the distribution system to accommodate harmonic currents. If you remove harmonic currents, phase currents will also fall.

The installation was a success. After installing the harmonic suppression system on transformer No. 1, rms neutral current dropped by 71%, with the third-harmonic current decreasing by 98% to only 5A. Current THD was down by 87% in the phases and rms phase currents were reduced by 44%.

This reduction in rms phase currents enabled Lasher to connect additional computer loads. Post installation infrared testing showed, even with more loads connected, transformer and distribution panel temperatures were significantly lower, which decreased the likelihood of transformer failure caused by overheating.

A preliminary cost analysis showed an estimated reduction of 8% in power dissipation as heat due to I2R losses in the transformer and wiring. The installation also saved the company the expense of the air conditioning that would have been necessary to remove this heat. The cost analysis projected a payback in less than two years. More importantly, the installation required only a few hours of downtime; whereas rewiring or replacing a transformer would have taken longer — and consumed more revenue.

Want to use this article? Click here for options!





Acceptable Use Policy
blog comments powered by Disqus

what's wrong here?

What's Wrong Here?

May 10, 2012 12:44 PM

What's Wrong Here?

Apr 19, 2012 10:09 AM

What's Wrong Here?

Apr 5, 2012 2:27 PM

View all What's Wrong Here?

product spotlight

EV charger tester

May 25, 2012 8:26 AM

EV charger tester

The Electrician is portable tester that verifies critical power and safety requirements of electric vehicle (EV) chargers...

View all 2012 Product Spotlights

Free Product Info

Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.

Recent Comments

More...


Social Media

More ways to stay informed...

follow us on twitter

Find us on Facebook

EC&M TV

Arlington CP9000

Arlington’s new 9” diameter ceiling cover plate is the neatest way to cover unused “high hat” cans. With no tools needed, installation couldn’t be faster!...

Arlington Gangable Boxes

Designed for new or retrofit applications, these snap-together gangable plastic boxes eliminate the need to construct a multiple-gang steel box out of several individual ones...

Listen
Sizing Gen-Sets: Facts, Hints, and Good Judgment
Listen

The complexities of today’s commercial or industrial facility, with their equipment environment of linear and nonlinear loads, places a whole new light on sizing engine-generator sets.

Understanding NEC Requirements for Solar Photovoltaic Systems
During this session, Mike Holt will address possible conflicts or confusing NEC requirements, provide tips on proper electrical installation techniques, and discuss the dangers related to improper installations. View this On Demand Webinar!

Top Code Changes: 2011 NEC
EC&M has partnered with NEC expert Mike Holt to present a one hour Webinar covering the top 2011 NEC Code Changes. This event will be broadcast live on the Web with streaming audio and PowerPoint slides allowing the audience to have real-time interaction with the guest speaker, Mike Holt. View this On Demand Webinar!

resources

product info icon

product info

tradeshow icon

tradeshow

research icon

research

industry links

industry links

rss icon

rss

Browse Back Issues

Browse Back Issues