Ground Testing Essentials

Proper grounding is essential to maintaining good power quality. Do you know the essential steps of doing a ground test?

The best way to become proficient with ground testing is to test often. You'll learn to recognize patterns of inconsistency and become adept at recognizing factors that produce inaccurate results. You'll learn to disregard test results skewed by environmental influences. Before you begin ground testing, make sure you understand these three essential elements.

  • Use a dedicated ground tester,

  • Understand the test and test environment, and

  • Place the probes properly.

Choosing the proper instruments. The digital multimeter (DMM) is a good tool, but not for measuring ground resistance. Two-point measurements with a DMM will give you the loop resistance as defined by the arbitrary points of connection, including all soil between those points. It also won't correct the presence of transient currents. So, use a device specifically designed to measure ground resistance.

Understanding the test is crucial to doing it right. The Figure (of original article) shows how a dedicated ground tester works. The instrument uses two precise measuring circuits (voltage and current), and combines their values through Ohm's Law to produce the desired measurement (resistance).

Understanding the test environment is crucial to getting a useful measurement. A ground test is never routine. Remember, the earth is not a defined circuit. However, it does provide a resistance environment surrounding the ground electrode. This resistance environment has a fixed nature, determined by the soil type, the structure of the electrode, and the electrical demands upon it. It also has a variable nature, determined by transient factors like moisture and temperature. Thus, you must measure the entire critical volume of soil surrounding the electrode: This is what influences the flow of fault current into the earth.

You establish the test circuits in the soil by strategically placing probes. Proper placement of the probes (in relation to moisture pockets, buried objects, etc.) is critical. You will probably need to experiment with probes in several locations to get a truly representative reading. Pay attention to probe spacing. If the potential probe is too close to the grounding electrode, your readings won't reflect all the resistance a fault would meet. If the current probe is too close, you'll be trying to make readings in conflicting electrical fields.

The current circuit has a square waveform that sets it apart from utility power harmonics. Thus, the ground tester can measure current without interference from transients. Likewise, the voltage (or potential) probe enables the tester to measure the drop over the soil to a probe's critical point of placement. A second set of terminals allows the instrument to complete both circuits.

The "Fall of Potential," or "three point method" references three points of earth contact set up by the ground electrode and the two probes. IEEE Standard #81 describes this method. This test is the recognized basis for ground testing in the United States.

You need such accuracy so you know your path to ground has low enough resistance to allow circuit protection devices to work properly. Further, to do fault calculations, you must know your earth resistance.

Consider these essentials the starting point to a successful ground testing program. The IEEE, ground tester manufacturers and grounding equipment vendors have more information. You can also visit www.ecmweb.com and www. ecmbooks.com.


Want to use this article? Click here for options!





Acceptable Use Policy
blog comments powered by Disqus

what's wrong here?

What's Wrong Here?

May 10, 2012 12:44 PM

What's Wrong Here?

Apr 19, 2012 10:09 AM

What's Wrong Here?

Apr 5, 2012 2:27 PM

View all What's Wrong Here?

product spotlight

EV charger tester

May 25, 2012 8:26 AM

EV charger tester

The Electrician is portable tester that verifies critical power and safety requirements of electric vehicle (EV) chargers...

View all 2012 Product Spotlights

Free Product Info

Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.

Recent Comments

More...


Social Media

More ways to stay informed...

follow us on twitter

Find us on Facebook

EC&M Whitepaper

Arc Mitigation –A Three-Step Approach

Did you know that an arc-flash incident hospitalizes 5-7 workers per day in North America, severely impacting processes and profitability with lost production? Download This Sponsored Whitepaper Today!

What's New in Residential Cabling?
Date: Wednesday, May 30, 2012
Time: 2:00pm ET


In this The Home Depot sponsored Low Voltage Webinar, Ron Kipper RCDD / NTS will discuss the need for compression style coaxial connectors and the migration of the entire CATV, Satellite and Audio / Video industry to them. Register Today!

Grounding Versus Bonding
Now Available On-Demand


In this 60-minute FREE webinar, Mike Holt of Mike Holt Enterprises, Inc. will explain the purpose of grounding and bonding as related to the most current requirements set forth in the 2011 NEC. Register to View On-Demand!

resources

product info icon

product info

tradeshow icon

tradeshow

research icon

research

industry links

industry links

rss icon

rss

Browse Back Issues

Browse Back Issues