Equipment Grounding: Know What to Expect!

To better understand the concept of equipment grounding, you should review two NEC definitions in Art. 100:

  • Ground. A conducting connection, whether intentional or accidental, between an electrical circuit or equipment and the earth, or to some conducting body that serves in place of the earth.

  • Grounding conductor. A conductor used to connect equipment or the grounded circuit of a wiring system to a grounding electrode or electrodes.

Also review the requirement that states in part:

Grounding of electrical equipment. Conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected to earth so as to limit the voltage to ground on these materials [Sec. 250-2(b)].

This concept seems simple: Connect metal parts of an electrical system to the earth to limit the voltage-to-ground on the metal parts. But where did the voltage come from and how are you limiting it?

As the Figure shows, you bond metal parts of an electrical system together and then ground the bonding system to earth to limit the voltage-to-ground — thus preventing destruction of electrical components as well as electric shock that can occur from superimposed voltage from lightning and voltage transients [Sec. 250-2(b)].

However, according to data from the insurance industry, failure to properly ground communications systems [Secs. 800-40(b), 810-12(f), 820-40(b) and 830-40(b)] has led to $500 million of property or equipment damage annually due to lightning or surges. Why? The resistance of the ground determines how effectively your grounding system can dissipate high-voltage surges into the earth. The impedance of the earth ground depends on the resistance of the electrodes, termination resistance, contact resistance of the electrodes to the adjacent earth, and the resistance of the body of earth surrounding the electrodes (soil resistivity).

The NEC does not require you to measure the ground resistance of the grounding electrode unless you use only a single ground rod. When you use two or more ground rods, the measured ground resistance can exceed 25 ohms [Sec. 250-56]. Therefore, to achieve and maintain a low-resistive ground, you must use special grounding configurations, design, and equipment and measuring devices. Failure to properly ground the metal parts of an electrical system to the earth can result in electric shock and fire. Electronic equipment can be destroyed by lightning, line surges, or other high-voltage transients.

Grounding metal parts to the earth does not assist in removing dangerous voltage from line-to-ground faults by opening the circuit overcurrent protection device for the systems that operate at less than 600V! Next month, we'll see why.






Acceptable Use Policy
blog comments powered by Disqus

what's wrong here?

What's Wrong Here?

May 10, 2012 12:44 PM

What's Wrong Here?

Apr 19, 2012 10:09 AM

What's Wrong Here?

Apr 5, 2012 2:27 PM

View all What's Wrong Here?

product spotlight

EV charger tester

May 25, 2012 8:26 AM

EV charger tester

The Electrician is portable tester that verifies critical power and safety requirements of electric vehicle (EV) chargers...

View all 2012 Product Spotlights

Free Product Info

Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.

Recent Comments

More...


Social Media

More ways to stay informed...

follow us on twitter

Find us on Facebook

EC&M Whitepaper

Arc Mitigation –A Three-Step Approach

Did you know that an arc-flash incident hospitalizes 5-7 workers per day in North America, severely impacting processes and profitability with lost production? Download This Sponsored Whitepaper Today!

What's New in Residential Cabling?
Date: Wednesday, May 30, 2012
Time: 2:00pm ET


In this The Home Depot sponsored Low Voltage Webinar, Ron Kipper RCDD / NTS will discuss the need for compression style coaxial connectors and the migration of the entire CATV, Satellite and Audio / Video industry to them. Register Today!

Grounding Versus Bonding
Now Available On-Demand


In this 60-minute FREE webinar, Mike Holt of Mike Holt Enterprises, Inc. will explain the purpose of grounding and bonding as related to the most current requirements set forth in the 2011 NEC. Register to View On-Demand!

resources

product info icon

product info

tradeshow icon

tradeshow

research icon

research

industry links

industry links

rss icon

rss

Browse Back Issues

Browse Back Issues