Code Forum

Here's exactly how and why you double the range (and dryer) loads on 3-phase distributions, what happens next, and how Example 5(a) integrates this process.

If you're having problems understanding National Electrical Code (NEC) requirements for 3-phase demand calculations, you're not alone. Recently, a reader asked a question on these calculations. Yes, he understood Sec. 220-19 correctly: determine the maximum number of ranges between any two phases; multiply that number by 2; and then refer to Table 220-19 for demand. However, this procedure didn't look like the examples at the end of the NEC. Here, Appendix D, Example 5(a) takes this demand value, divides it by 2 for a per-phase demand, and multiplies that number by 3 for equivalent 3-phase load. When referring to these calculations in Sec. 220-19, our friend also wondered if the NEC intended the word "range" as the key word. Did it mean counter-mounted cooktops and wall-mounted ovens don't apply to the 3-phase procedure? For instance, suppose the 10 units in Example 5(a) consisted of 10 5kW cooktops and 10 4kW wall-mounted ovens.

EC&M panel's response. The procedure in Example D5(a) is correct. You connect ranges, like any other load, between two phase conductors.

Technically, a phase isn't a wire; it's a transformer winding between two wires. This means when you calculate loading on a "phase conductor," you actually figure how much load, in amperes, results from the two phase loads common to that conductor.

In this case, the Code simplifies the problem by just doubling the highest loaded phase. That's the number to use when you go to the demand table. Once you determine the total demand load from this table, then you split it in half to get the calculation for each winding. Ignoring the square root of 3 for the moment, all you're doing is reversing the doubling procedure you started with. So, the total 3-phase load is the arithmetic sum for all three phases of what you just determined, or triple the amount on a single-phase winding. Remember, we're only working with load so far. We haven't addressed ampere loading on a conductor yet. Example D5(a) carries the total load in volt-amperes throughout load calculations. At the end, you divide by the product of voltage and the square root of 3 to get the number of amperes on one of the "phase" conductors.

Still not convinced? Go back to the range load on one of the phases and look at how it relates to a similar load on an adjacent phase. The loads on phase connections A-B and B-C add vectorially on the common conductor "B," for example. For equal loads (A-B and B-C), you do not add them arithmetically. The common conductor only sees one of those phase loads multiplied by the square root of 3. Multiplying a number by 3 (as in the Code example) and then dividing by the square root of 3 at the end is exactly the same as multiplying by the square root of 3 at this point. The Code example simply postpones using the square root of 3 and voltage factors until the end, so you only need to use them once.

For cooktops separate from other components, Note 4 to Table 220-19 allows for a single branch circuit to connect the elements. This reflects a similar allowance in Sec. 210-19(c) Ex. 1. Sec. 220-10, typically requiring that a feeder reflect the loading on the branch circuits it supplies. Here, combine the cooktop and oven in each dwelling and treat the combination as a range. If you wire each appliance on its own circuit, apply Note 3 to Table 220-19.




Editor's Note:

These answers are given by our panel of experts. This author chairs the panel. Other panel members include: Bill Summers, James Stallcup, Dan Leaf, and Joe Ross.

The opinion expressed is that of the panel. If a panelist disagrees with the majority opinion, his explanation is printed following the answer. Although authoritative, the answers printed here are not, and cannot be relied on as formal interpretations of the NEC.


Want to use this article? Click here for options!





Acceptable Use Policy
blog comments powered by Disqus

what's wrong here?

What's Wrong Here?

May 10, 2012 12:44 PM

What's Wrong Here?

Apr 19, 2012 10:09 AM

What's Wrong Here?

Apr 5, 2012 2:27 PM

View all What's Wrong Here?

product spotlight

EV charger tester

May 25, 2012 8:26 AM

EV charger tester

The Electrician is portable tester that verifies critical power and safety requirements of electric vehicle (EV) chargers...

View all 2012 Product Spotlights

Free Product Info

Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.

Recent Comments

More...


Social Media

More ways to stay informed...

follow us on twitter

Find us on Facebook

EC&M Whitepaper

Arc Mitigation –A Three-Step Approach

Did you know that an arc-flash incident hospitalizes 5-7 workers per day in North America, severely impacting processes and profitability with lost production? Download This Sponsored Whitepaper Today!

What's New in Residential Cabling?
Date: Wednesday, May 30, 2012
Time: 2:00pm ET


In this The Home Depot sponsored Low Voltage Webinar, Ron Kipper RCDD / NTS will discuss the need for compression style coaxial connectors and the migration of the entire CATV, Satellite and Audio / Video industry to them. Register Today!

Grounding Versus Bonding
Now Available On-Demand


In this 60-minute FREE webinar, Mike Holt of Mike Holt Enterprises, Inc. will explain the purpose of grounding and bonding as related to the most current requirements set forth in the 2011 NEC. Register to View On-Demand!

resources

product info icon

product info

tradeshow icon

tradeshow

research icon

research

industry links

industry links

rss icon

rss

Browse Back Issues

Browse Back Issues