Yes, it’s true. Sec. 240-3(d) (the former Table 310-16 obelisk note) doesn’t apply to pure motor circuit conductors sized in accordance with Sec. 430-22(a).

The drawing you see to the right (available in print version) appears in the December 1998 issue of EC&M, on page 40, as well as in my NEC Illustrated Changes books. It shows a 2-hp motor fed from a 30A circuit breaker and, as covered in the associated text, No. 14 THWN wires. The 1998 article states the wire was sized per Sec. 430-22(a).

The submitter believes the No. 14 wire is incorrect, arguing Sec. 430-22(a) says the conductor ampacity needs to be a minimum of 125% of the motor rating, as determined by Sec. 430-6(a)(1). This section requires the conductors to be selected in accordance with Sec. 310-15(b) or 310-15(c).

Sec. 310-15(b) requires you to use ampacity tables for conductors rated 0 to 2000V (which include the 600V-rated conductors used). Tables 310-16 and 310-17 have an asterisk notation that refers to Sec. 240-3. This section requires conductors to be protected by an overcurrent device, which limits the current to the ampacity of the conductor. Subparagraph (d) to Sec. 240-3 requires the overcurrent device for small conductors to be limited to 15A for No. 14, No. 20A for No. 12, and 30A for No. 10.

The submitter concludes that following this, the minimum conductor size would be No. 10, not No. 14—based on the 30A circuit breaker. He adds a No. 10 conductor meets requirements of Sec. 430-22(a) because it exceeds the minimum of 125% of motor full load current.

The response. The submitter is entirely incorrect. The former obelisk note to the ampacity tables, now Sec. 240-3(d), has never applied if other sections of the Code make alternate provisions. In its new location (Sec. 240-3), this concept is clear in the parent language, which refers to Sec. 240-3(a) through (g). Included therein is Sec. 240-3(g), which in part includes motors. One of the reasons the Usability Committee recommended moving the obelisk note into Art. 240 was to make this point more obvious.

The overcurrent protection for this circuit is divided. The circuit breaker in this instance provides short-circuit protection only. The running overload protection for the motor provides the overload protection. The reason Sec. 430-22(a) uses the 125% parameter is to correlate with Sec. 430-32(a)(1), which also uses 125%. With the motor and its conductors thus fully protected against overload, the only remaining issue is short-circuit and ground-fault protection, and the ratios in Table 430-152 do just that.

This question comes up often. I’d hoped the relocation into Sec. 240-3 would solve the problem, but perhaps not. Be assured, however, there has never been any intention to apply the former obelisk notes to motor circuits, nor is there in the ’99 NEC, now that the rules appear in Sec. 240-3(d).


Want to use this article? Click here for options!





Acceptable Use Policy
blog comments powered by Disqus

what's wrong here?

What's Wrong Here?

Feb 2, 2012 7:54 PM

What's Wrong Here?

Jan 19, 2012 4:06 PM

What's Wrong Here?

Jan 5, 2012 11:53 AM

View all What's Wrong Here?

product spotlight

Labeling tool

Feb 10, 2012 7:58 AM

Labeling tool

The Rhino 4200 labeling tool features one-touch “hot keys” that quickly create and format wire/cable wraps, flags, fixed-length labels and more...

View all 2012 Product Spotlights

Free Product Info

Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.

Recent Comments

More...


Social Media

More ways to stay informed...

follow us on twitter

Find us on Facebook

EC&M TV

Arlington CP9000

Arlington's new 9" diameter ceiling cover plate is the neatest way to cover unused "high hat" cans. With no tools needed, installation couldn't be faster!...

Arlington Gangable Boxes

Designed for new or retrofit applications, these snap-together gangable plastic boxes eliminate the need to construct a multiple-gang steel box out of several individual ones...

Understanding NEC Requirements for Solar Photovoltaic Systems
During this session, Mike Holt will address possible conflicts or confusing NEC requirements, provide tips on proper electrical installation techniques, and discuss the dangers related to improper installations. View this On Demand Webinar!



resources

product info icon

product info

tradeshow icon

tradeshow

research icon

research

industry links

industry links

rss icon

rss

Browse Back Issues

Browse Back Issues