Belleville Blues?


Bus bar connections are critical in electrical installations. I want to clarify some items in the May “Back to Basics” article.

Most bus bars are silver or tin-plated—not copper plated. The purpose of plating is to reduce oxidation, thus improving the connections. This thin plating can scrape off easily. Abrasive cleaning will likely remove the plating, leading to hot joints and potential failure. A solvent cleaning process is the preferred method.

The method suggested for maintaining joint tightness may be confusing. The article said, “Manufacturers have determined...you get the most reliable connection by using steel bolts and steel flat washers.” Many UL standards require using spring washers (Belleville) or lockwashers and a flat washer. Our tests show the coolest, most reliable joint is with a Belleville washer. A properly torqued Belleville washer compensates for the different thermal expansion rates of the steel bolt and bus bars.

You shouldn’t flatten the Belleville. You should compress it to 80% of its free height to give you room for expansion and contraction. Based on our experience, properly designed and torqued Belleville washer joints will not work loose in the field.

Finally, the article states: “don't reuse any locking devices, especially Belleville washers.” This probably applies to split ring lockwashers. These lockwashers lose their “bite” after reuse. Yet, you can reuse properly designed and torqued Belleville washers.

Frederick A. Reker, P.E.
Square D Co.
Nashville, TENN.




Author's Reply

Every point Mr. Reker makes is correct. I did not suggest you must file a bus bar before assembling. Usually, solvent is all you need. However, many people do use abrasive methods. Sometimes, these are necessary, sometimes not. The article points out proper abrasive cleaning techniques, in either case.

It’s true Belleville washers normally do not work loose in the field. However, anything can work loose under vibration, heat, corrosion, or other factors—causing catastrophic results. Thus, an annual visual inspection is good preventive maintenance. I must reinforce Reker’s point that while other washers usually lose their “bite,” the Belleville washer is like a pit bull when it comes to clamping.

The mention of steel bolts and flat washers was not to the exclusion of Belleville washers or other locking devices. A flat washer is not a locking device—you must use it with a locking device.

Reker also addresses locking device reuse. I contacted two manufacturers, and they said reuse is application- specific. The differentiating factor is whether your Belleville has sharp edges or not (most Bellevilles do not). Belleville washers do not lose spring capacity. If a manufacturer says to reuse a Belleville, then doing so should result in no performance loss whatsoever. The article’s statement about not reusing a Belleville is incorrect in most circumstances, but correct in some. The statement would have been better had it read: “If you are unsure about your particular style of Belleville washer, then it is better to replace it than to reuse it where you shouldn't.” —M.L.L.


Want to use this article? Click here for options!





Acceptable Use Policy
blog comments powered by Disqus

what's wrong here?

What's Wrong Here?

May 10, 2012 12:44 PM

What's Wrong Here?

Apr 19, 2012 10:09 AM

What's Wrong Here?

Apr 5, 2012 2:27 PM

View all What's Wrong Here?

product spotlight

EV charger tester

May 25, 2012 8:26 AM

EV charger tester

The Electrician is portable tester that verifies critical power and safety requirements of electric vehicle (EV) chargers...

View all 2012 Product Spotlights

Free Product Info

Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.

Recent Comments

More...


Social Media

More ways to stay informed...

follow us on twitter

Find us on Facebook

EC&M Whitepaper

Arc Mitigation –A Three-Step Approach

Did you know that an arc-flash incident hospitalizes 5-7 workers per day in North America, severely impacting processes and profitability with lost production? Download This Sponsored Whitepaper Today!

What's New in Residential Cabling?
Date: Wednesday, May 30, 2012
Time: 2:00pm ET


In this The Home Depot sponsored Low Voltage Webinar, Ron Kipper RCDD / NTS will discuss the need for compression style coaxial connectors and the migration of the entire CATV, Satellite and Audio / Video industry to them. Register Today!

Grounding Versus Bonding
Now Available On-Demand


In this 60-minute FREE webinar, Mike Holt of Mike Holt Enterprises, Inc. will explain the purpose of grounding and bonding as related to the most current requirements set forth in the 2011 NEC. Register to View On-Demand!

resources

product info icon

product info

tradeshow icon

tradeshow

research icon

research

industry links

industry links

rss icon

rss

Browse Back Issues

Browse Back Issues