The Basics of Voltage Imbalance

Electrical equipment; especially motors and their controllers; will not operate reliably on unbalanced voltages in a 3-phase system. Generally, the difference between the highest and the lowest voltages should not exceed 4% of the lowest voltage. Greater imbalances may cause overheating of components; especially motors; and intermittent shutdown of motor controllers. Motors operated on unbalanced voltages will overheat, and many overload relays can't sense the overheating. In addition, many solid-state motor controllers and inverters include components that are especially sensitive to voltage imbalances.

How much imbalance is too much? Let's look at an example. Suppose the lowest voltage on a 3-phase circuit is 230V, while another phase is 235V, and the third phase is 240V. Is this a significant voltage imbalance? Let's use the 4% rule to see.

Four percent of the lowest voltage (230V) is 9.2V (230V24%49.2V). The difference between the highest voltage (240V) and the lowest voltage (230V) is 10V. Therefore, these voltages have too great an imbalance. Why? Because the 10V difference is greater than four percent of the lowest voltage (9.2V).

You can use a more precise procedure for calculating voltage imbalance. The first step is to calculate the average voltage by adding all three phases and dividing by 3. In our example, the average is 235V: You add the voltages to get your total. 230V`235V`240V 4705V. Then you divide by the number of phases. 705V / 34235V.

Next, add up the absolute differences between each phase voltage and the average voltage. In this case, the difference between the average voltage and 230V is 5V. The difference between the average and itself is 0V; and the difference between the average and 240V is 5V. Adding up the differences, we get 10V. And that 10V is what we call the total imbalance.

Now divide the total imbalance in half to get an adjusted imbalance. Half of 10V is 5V. Finally, divide the adjusted imbalance into the average voltage to get a percentage imbalance. In this case, 5V / 235V40.021. That is 2.1% imbalance.

Reliable, long-term operation of most electrical equipment requires a voltage imbalance of less than two percent; which means your system has too much imbalance.

If you find voltage imbalances in your facility, the first place to look is not the power company. Instead, look for electrical distribution systems in which one leg of a 3-phase supply powers both single-phase and 3-phase loads. You may find single phase loads not evenly balanced across the phases. Or, look for in-line reactors installed to correct imbalances. These reactors usually have taps for adjustment, and somebody may have adjusted them. Or, the imbalance they originally corrected may have shifted over time. Circuits with tapped reactors rarely stay in balance indefinitely.

Now, here's a practice question. You go out onto the floor and find a 460V motor with phase voltages of 458V, 465V, and 480V. Is there a problem or not? There sure is.

Lowest voltage is 458V. First, calculate your four percent. 0.042458V 418.32V. The difference between the highest voltage (480V) and the lowest voltage (458V) is 22V (480-458). Since the difference (22V) is greater than 4% of the lowest voltage (18.32V), the phases are too far out of balance to ensure continued, reliable operation of electrical equipment.


Want to use this article? Click here for options!





Acceptable Use Policy
blog comments powered by Disqus

what's wrong here?

What's Wrong Here?

May 10, 2012 12:44 PM

What's Wrong Here?

Apr 19, 2012 10:09 AM

What's Wrong Here?

Apr 5, 2012 2:27 PM

View all What's Wrong Here?

product spotlight

EV charger tester

May 25, 2012 8:26 AM

EV charger tester

The Electrician is portable tester that verifies critical power and safety requirements of electric vehicle (EV) chargers...

View all 2012 Product Spotlights

Free Product Info

Our Product Information site is the ultimate online resource for products and services offered by Advertisers featured in our Magazine. This service is provided as a quick and easy way to request Product Information online. Get FREE product information now.

Recent Comments

More...


Social Media

More ways to stay informed...

follow us on twitter

Find us on Facebook

EC&M Whitepaper

Arc Mitigation –A Three-Step Approach

Did you know that an arc-flash incident hospitalizes 5-7 workers per day in North America, severely impacting processes and profitability with lost production? Download This Sponsored Whitepaper Today!

What's New in Residential Cabling?
Date: Wednesday, May 30, 2012
Time: 2:00pm ET


In this The Home Depot sponsored Low Voltage Webinar, Ron Kipper RCDD / NTS will discuss the need for compression style coaxial connectors and the migration of the entire CATV, Satellite and Audio / Video industry to them. Register Today!

Grounding Versus Bonding
Now Available On-Demand


In this 60-minute FREE webinar, Mike Holt of Mike Holt Enterprises, Inc. will explain the purpose of grounding and bonding as related to the most current requirements set forth in the 2011 NEC. Register to View On-Demand!

resources

product info icon

product info

tradeshow icon

tradeshow

research icon

research

industry links

industry links

rss icon

rss

Browse Back Issues

Browse Back Issues