NEC Feeders

1 reply [Last post]
kendad's picture
Offline
Joined: 2014-03-08

Smallest feeder conductor allowed by Code is  _____ amps, as noted in Article or Section _____?

sparky377's picture
Offline
Joined: 2013-10-07

See Section 215.2(A)(1): requires an ampacity not less than 125% of the continuous plus the non-continuous load. In theory, you could have a 15A feeder, which would then be 14 AWG in accordance with 310.15(B).