Understanding Harmonic Indices
Apr 1, 2008 12:00 PM, By John DeDad, Senior Director; Editorial and EC&M Development
The power quality industry has developed certain index values that help us assess the quality of service as it relates to distortion caused by the presence of harmonics. These values, or harmonic indices, serve as a useful metric of system performance. The two most frequently used are total harmonic distortion (THD) and total demand distortion (TDD). They are measures of the effective value of a waveform and can be applied to both current and voltage.
THD
According to the book “Electrical Power Systems Quality” by Dugan, McGranaghan, Santoso, and Beaty (ISBN 0-07-138622-X), THD is a measure of the effective value of the harmonic components of a distorted waveform. It can be calculated for either current or voltage. Although many of today's test and measurement instruments can provide THD values, it's still important to understand the calculation that derives THD. The basic equation is as follows:
where M
Don't be intimidated by this equation. Basically, it's stating that THD is equal to the square root of the sum of the squares of each rms component M from the harmonic after the fundamental (h greater than 1) to the highest harmonic component (h
The power quality industry most often uses the THD index to describe voltage harmonic distortion and always references harmonic voltages to the fundamental value of the waveform at the time of measurement, as defined by the equation below:
Basically, this equation is saying voltage THD is equal to the square root of the sum of the squares of each rms harmonic voltage component from the harmonic after the fundamental (h = 2) to the highest harmonic voltage component (h=∞), divided by the rms value of the fundamental voltage component (V
This makes sense because the fundamental voltage varies only by a few percent, so any reference of voltage THD, relative to the fundamental, is nearly always a meaningful number.
Table 1. Harmonic voltage spectrum example.
The book “Power Quality in Electrical Systems” by Kusko and Thompson (ISBN-10:0-07-147075-1) provides an example of how to manually calculate THD. Suppose we have a harmonic voltage spectrum as listed in Table 1. Using Equation 1, we can calculate the THD for this scenario:
TDD
As previously mentioned, we can characterize current distortion levels with a THD value, but this can be misleading. According to the book “Electrical Power Systems Quality,” a small current can have a high THD but not be a significant threat. For example, many adjustable-speed drives will exhibit high THD values for the input current while operating at very light loads. This shouldn't be a concern, because the magnitude of harmonic current would be low in this instance, even though its relative current distortion is quite high.
Responding to such scenarios, some analysts have referred to THD as the fundamental of the peak demand load current rather than the fundamental of the present sample. This is called total demand distortion, or TDD. Contrary to popular belief, TDD and not THD serves as the basis for the guidelines in IEEE 519, “Recommended Practices and Requirements for Harmonic Control in Electrical Power Systems.” In fact, IEEE 519 defines TDD as “the total root-sum-square harmonic current distortion, in percent of the maximum demand load current.” The following equation defines TDD:
where I
According to the book “Harmonics and Power Sources” by De La Rosa (ISBN 9780849330162), weak power sources with large demand current, relative to the rated current, will tend to show greater waveform distortion. On the other hand, stiff power sources operating at low demand currents will show decreased waveform distortion.
There are two ways in which to measure I
IEEE 519 and TDD
Table 2. Replication of IEEE 519 Table 10.1, “Basis for Harmonic Current Limits.” Reprinted with permission of IEEE.
The main function of IEEE 519 is to control the design of power harmonic filters in electrical systems. It does so by including harmonic voltage limits (Table 10.1, as replicated in Table 2) and current distortion limits (Table 10.3, as replicated in (click here to see Table 3).
Table 10.1 sets the maximum individual frequency voltage harmonics (percent) for loads connected to the PCC, as a function of the size of the load. The measure of size is determined by a ratio called the “short-circuit ratio,” or SCR, which is the ratio of the maximum short-circuit current at the PC (I
Now, to achieve these voltage harmonic limits, IEEE 519 sets limits (per its Table 10.3) on the amount of harmonic currents injected into the PCC, as a function of the size of the load. For example, for a load with an I
Although the concept isn't new, harmonic distortion continues to be a main concern of engineers in the various stages of energy use within the electrical industry. The increasing use of nonlinear loads is keeping harmonic distortion in facility and utility distribution networks on the rise.