Short-Circuit Calculation Methods
What is in this article?:
The task may seem overwhelming at first, but following a methodical step-by-step procedure can keep you from getting tripped up
All electrical systems are susceptible to short circuits and the abnormal current levels they create. These currents can produce considerable thermal and mechanical stresses in electrical distribution equipment. Therefore, it's important to protect personnel and equipment by calculating short-circuit currents during system upgrade and design. Because these calculations are life-safety related, they're mandated by 110.9 of the NEC, which states:
“Equipment intended to interrupt current at fault levels shall have an interrupting rating sufficient for the nominal circuit voltage and the current that is available at the line terminals of the equipment. Equipment intended to interrupt current at other than fault levels shall have an interrupting rating at nominal circuit voltage sufficient for the current that must be interrupted.”
When you apply these requirements to a circuit breaker, you must calculate the maximum 3-phase fault current the breaker will be required to interrupt. This current can be defined as the short-circuit current available at the terminals of the protective device.
You can assume that 3-phase short circuits are “bolted,” or have no impedance. In addition, a 3-phase short circuit can be considered a balanced load, which means you can use a single-phase circuit to analyze one of the phases and the neutral.
Distribution equipment, such as circuit breakers, fuses, switchgear, and MCCs, have interrupting or withstand ratings defined as the maximum rms values of symmetrical current. A circuit breaker can't interrupt a circuit at the instant of inception of a short. Instead, due to the relay time delay and breaker contact parting time, it will interrupt the current after a period of five to eight cycles, by which time the DC component will have decayed to nearly zero and the fault will be virtually symmetrical.
Closing a breaker against an existing fault makes it possible to intercept the peak of the asymmetrical short-circuit current, which is greater than the rms value of the symmetrical current. For this reason, equipment is also tested at a particular test X/R ratio value typical to a particular electrical apparatus, such as switchgear, switchboards, or circuit breakers, and is designed and rated to withstand and/or close and latch the peak asymmetrical current described above.
Fault analysis is required to calculate and compare symmetrical and asymmetrical current values in order to select a protective device to adequately protect a piece of electrical distribution equipment.