An Undistorted Look at Harmonics
How can you minimize harmonic distortion? Is the concern financial, or is your equipment at risk? Here are some basics you need to know. With so much equipment and knowledge available in this industry, specialization is sometimes necessary. But even with specialized training, many new technicians still lack the hands-on experience to troubleshoot power quality problems. Added to these concerns, we're
Discuss this Article 1
James Connell (not verified)
on Feb 27, 2013
Improper neutral to neutral connections can cause harmonics. For example two neutrals tied together where one is a normal power circuit and the other from an emergency power circuit and each are derived from different transformers.
Improper neutral to ground connections can cause harmonics.
I've seen where these improper connections will shorten the life span of lighting ballasts & sensitive electronic equipment.
There are two ways that I know of how to trace the improper connection.
1. If power can not be turned off use the "Net Zero Current Method" by taking an amp clamp around all the wires and you should read zero. There are some good articles on the internet that go into detail. This can be a long arduous process.
2. Turn power off feeding the panel. Disconnect each branch neutral from the neutral bus bar and ohm it to ground. There should be on open circuit reading between the disconnected neutral and ground. If you your meter detects a connection then you know you have an improper neutral to ground or neutral to neutral. This is a quick way to check out an electrical system.