Conductors - Art. 310
What is the current-carrying ampacity of each of nine No. 12 THHN copper conductors installed in ¾-in. EMT? (Assume all conductors are current-carrying.)
a. 17A
b. 21A
c. 25A
d. 28A -
What is the current-carrying ampacity of each of six No. 14 THHN copper conductors routed through an ambient temperature of 105°F?
a. 17.4A
b. 18.6A
c. 19.8A
d. 21.4A -
What is the current-carrying ampacity of each of sixteen No. 12 THHN copper conductors, with diversity, located in the same raceway? (Assume only half of the conductors are current-carrying.)
a. 17A
b. 18A
c. 20A
d. 21A -
What is the current-carrying ampacity of each of twelve No. 12 THHN copper conductors, if routed in a raceway where there is a total of 16 current-carrying conductors?
a. 17.2A
b. 18.4A
c. 19.6A
d. 21.2A
answers and discussion
(b), 21A. Cables or raceways enclosing four or more current-carrying conductors are required to be derated per Sec. 310-15(b)(2)(a). The NEC considers all ungrounded (phase) conductors to be current-carrying. Neutrals for Wye systems are considered current-carrying if the major portion of the load (more than 50%) consists of harmonic currents [Sec. 310-15(b)(4)(c)].
Step 1: Find amperage of each conductor per Table 310-16. No. 12 THHN cu. = 30A.
Step 2: Find derating factor per Table 310-15(b)(2)(a). 9 conductors requires a 70% derating factor.
Step 3: Recalculate amperage, per Table 310-15(b)(2)(a). 30A × 70% = 21A.
Solution: The ampacity of each conductor is 21A.
Stallcup's Code Loop: Secs. 110-14(c), 310-15(b)(2)(a), and 310-15(b)(4)(c), and Tables 310-16 and 310-15(b)(2)(a).
(a), 17.4A. See explanation for Questions 1 and the following:
Conductors routed through ambient temperatures exceeding 86°F must be derated according to the correction factors listed in Table 310-16. The derating factors are listed in the ampacity correction factor at the bottom of Table 310-16. Select the derating factors based on the ambient temperature the conductors are exposed to.
Step 1: Find amperage of conductors per Table 310-16. No. 14 THHN cu. = 25A
Step 2: Find derating factor for multiple conductors per Table 310-15(b)(2)(a). 6 conductors requires an 80% derating factor.
Step 3: Find derating factor for ambient temperature per Table 310-16. 105°F requires an 87% derating factor.
Step 4: Recalculate amperage per Tables 310-15(b)(2)(a) and 310-16. 25A × 80% × 87% = 17.4A.
Solution: The ampacity of each conductor is 17.4A.
(d), 21A. A 50% load diversity can be applied to a conductor ampacity when all the conductors are not loaded at the same time, if allowed by the authority having jurisdiction (AHJ).
Step 1: Find amperage for eight current-carrying conductors per Table 310-16. No. 12 THHN cu. = 30A
Step 2: Find derating factor per Table B-310-11 in Appendix B. 16 conductors requires a 70% derating factor.
30A × 70% = 21A
Solution: The ampacity of each conductor is 21A, however, only eight at any given time can have this ampacity rating.
Stallcup's Code Loop: Sec. 110-14(c), and Tables 310-16 and B-310-11.
(a), 17.2A. You can apply diversity to more than half of the conductors in a raceway or cable if they are limited to a certain calculated value.
Step 1: Apply formula for 12 conductors per Tables B-310-11 and 310-16.
A2 = √(0.5 × N/E) × A1, where A1= ampacity of conductor from Table 310-316 multiplied by the appropriate adjustment factor in Table B-310-11
A2 = √(0.5 × 16/12) × 30A × 0.7
A2 = 17.2ASolution: The ampacity of each conductor is 17.2A.