Quizzes on the Code
Choose the best answer: 1. What is the full-load current (FLC) rating of a 50 hp, 460V, 3-phase, Design B, squirrel-cage induction motor (motor nameplate FLA is 61.5A)? (a) 60A (b) 65A (c) 68A (d) 70A 2. What is the locked-rotor current (LRC) rating of a 50 hp, 460V, 3-phase, Design B, squirrel-cage induction motor? (a) 363A (b) 385A (c) 400A (d) 515A 3. What size time delay fuse (TDF) is required
(a) 60A
(b) 65A
(c) 68A
(d) 70A
(a) 363A
(b) 385A
(c) 400A
(d) 515A
3. What size time delay fuse (TDF) is required to start and protect a 50 hp, 460V, 3-phase, Design B, squirrel-cage induction motor per the following?
Part 1. Size the minimum (round down) TDF per Table 430-152.
(a) 110A
(b) 125A
(c) 150A
(d) 175A
Part 2. Size the next (round up) TDF per Sec. 430-52(c)(1), Ex. 1.
(a) 110A
(b) 125A
(c) 150A
(d) 175A
Part 3. Size the maximum TDF per Sec. 430-52(c)(1), Ex. 2(b).
(a) 110A
(b) 125A
(c) 150A
(d) 175A
Part 4. Start the motor with the smallest TDF per Table 430-151.
(a) 80A
(b) 90A
(c) 100A
(d) 110A
Answers and Discussion
1. (b). Except for sizing the overload protection, Sec. 430-6(a)(1) requires the FLC in amps from Table 430-150 to be used for sizing the elements of a motor circuit.
Stallcup’s Code Loop: Sec. 430-6(a)(1) and Table 430-150.
2. (a). Sec. 430-7(a)(9) mentions the Design letters of motors as B, C, D, or E. Refer to Table 430-151 for the LRC in amps to be used as starting currents of motors.
3. Part 1. (a). Use Table 430-152 and Sec. 430-52(c)(1) to select the minimum size TDF rating. However, you can use any size TDF that will start and run the motor.
Step 1: First, find the FLA per Sec. 430-6(a)(1) and Table 430-150.
50 hp = 65A
Step 2: Then, find the proper percentage per Sec. 430-52(c)(1) and Table 430-152.
Minimum size = 175%
Step 3: Then, calculate the minimum size per Sec. 430-52(c)(1).
65A x 175% = 113.75A
Step 4: Now, select the proper size TDF per Sec. 240-6(a).
Solution: The minimum size time delay fuse is 110A.
Stallcup’s Code Loop: Sec. 430-6(a)(1), Table 430-150, Sec. 430-52(c)(1), Table 430-152, and Sec. 240-6(a).
Part 2. (b). Sec. 430-52(c)(1), Ex. 1 allows the next size TDF to be used above 113.75A (round up), which is 125A. Note: The round up method is the size most often used.
Part 3. (b). Table 430-152 and Sec. 430-52(c)(1), Ex. 2(b) are used to select the maximum size TDF rating. However, you can use any size TDF that will start and run the motor.
50 hp = 65A
Step 2: Then, find the proper percentage per Sec. 430-52(c)(1), Ex. 2(b) and Table 430-152.
Maximum size = 225%
Step 3: Then, calculate the maximum size per Sec. 430-52(c)(1).
65A x 225% = 146.25A
Solution: The maximum size time delay fuse is 125A.
Stallcup’s Code Loop: Sec. 430-6(a)(1), Table 430-150, Sec. 430-52(c)(1), Ex. 2(b), Table 430-152, and Sec. 240-6(a).
Part 4. (a). Based on the answer in question (2), we know the LRC rating of this motor is 363A. We also know a TDF will normally hold five times its rating. Since 80A x 5 = 400A is greater than 363A, an 80A TDF will typically allow a motor with an LRC of 363A to start and run. (See Secs. 430-57, Ex. and 430-55.)
Note: Minimum and maximum sizes are used as a starting point to select the OCPD (smaller sizes can be selected).