• Use of Strike Termination Devices
    The installation requirements for a grounding electrode system and grounding electrode conductor are shown in Part III of Art. 250 in the 2011 NEC.
    July 23, 2014
    The grounding electrode used for grounding strike termination devices in a lightning protection system can be used as a grounding electrode system for the buildings or structures.
    a) True
    b) False
    See answer and applicable Code reference
    The correct answer is: b) False
    The installation requirements for a grounding electrode system and grounding electrode conductor are shown in Part III of Art. 250 in the 2011 NEC. As noted in 250.60, "Conductors and driven pipes, rods, or plate electrodes used for grounding strike termination devices shall not be used in lieu of the grounding electrodes required by 250.50 for grounding wiring systems and equipment. This provision shall not prohibit the required bonding together of grounding electrodes of different systems."