Sizing Equipment Grounding Conductors for PV Modules
The grounding requirements for PV systems are outlined in Part V of NEC Article 690.
Aug. 18, 2014
Where exposed and subject to physical damage, PV array equipment grounding conductors smaller than 4 AWG must be protected by raceway or cable armor.
a) True
b) False
See answer and applicable Code reference
The correct answer is: b) False
The provisions of Art. 690 apply to solar photovoltaic (PV) electric systems. The grounding requirements for PV systems are outlined in Part V of this Article. As per Sec. 690.46, "Equipment grounding conductors for photovoltaic modules smaller than 6 AWG shall comply with 250.120(C)."