The rules for pull and junction boxes, as well as conduit bodies, are outlined in Sec. 314.28 of the 2011 NEC.
Where angle or U pulls are made, the distance between each raceway entry inside the box or conduit body and the opposite wall of the box or conduit body shall not be less than _____ times the trade size of the largest raceway in a row plus the sum of the trade sizes of the remaining raceways in the same wall and row.
a) six
b) eight
c) ten
d) twelve
See answer and applicable Code reference
The correct answer is: a) six
The rules for pull and junction boxes, as well as conduit bodies, are outlined in Sec. 314.28 of the 2011 NEC. As noted in the first sentence of 314.28(A)(2), "Where splices or where angle or U pulls are made, the distance betwwen each raceway entry inside the box or conduit body and the opposite wall of the box or conduit body shall not be less than six times the metric designator (trade size) of the largest raceway in a row."