• Flexible Cords Used in Class I Locations
    NEC rules for flexible cords used in Class I Locations
    March 18, 2014
    In Division 1 or Division 2 locations where the boxes, fittings, or enclosures are required to be explosionproof, if a flexible cord is used it must terminate with a cord connector or attachment plug listed for the location, or a cord connector or attachment plug with a seal that is listed for the location. In Division 2 locations, where explosionproof equipment is not required, the cord can terminate _____.
    a) with a listed cord connector
    b) with a listed attachment plug
    c) in a splice of any manner
    d) a or b
    See answer and applicable Code reference
    The correct answer is: d) a or b
    Article 501 focuses on Class I Locations. Section 501.140 contains the requirements for Flexible Cords, Class I, Divisions 1 and 2.
    As per 501.140(B)(4), the flexible cord shall be terminated with a cord connector or attachment plug listed for the location, or a cord connector installed with a seal listed for the location.