"If you run DC input PV system conductors and AC inverter output conductors inside a building or structure, run them in metal raceway, Type MC cable, or metal enclosure [690.31(E)]. "
There has been quite a bit of discussion to the second part of this comment. AC inverter output conductors do not apply to section 690.31(E) as it now specifically only relates to DC. I cannot find any section in the code that states AC inverter output conductors must be run in a metal raceway inside a building to the disconnect. Is there such provision?
on Sep 18, 2012
Hello,
Your interpretation is correct. Section 690.31(E) would not apply to the Inverter Output conductors based on the title of 690.31(E).