Question: Grounding electrode conductors smaller than _____ shall be protected in rigid metal conduit, IMC, PVC conduit, electrical metallic tubing, or cable armor.
a) 10 AWG
b) 8 AWG
c) 6 AWG
d) 4 AWG
See answer below.
Answer: c) 6 AWG
Section 250.64(B)(3) states, "Grounding electrode conductors smaller than 6 AWG shall be protected in RMC, IMC, Schedule 80 PVC, RTRC-XW, EMT, or cable armor."