Photo 18091581 © Jaypetersen | Dreamstime.com
dreamstime_m_18091581
Understanding NEC Definitions for Conduit
April 2, 2024
Article 100 defines "raceway," and conduit is one type of raceway "family."
What is conduit? And would you say this definition from NEC Art. 100 is correct? “An enclosed channel designed expressly for holding wires, cables, or busbars, with additional functions as permitted within this Code.” However, that’s not the definition of “conduit.” In fact, you won’t find “conduit” defined in Art. 100. This definition is actually for raceway.
Conduit is just one “family” of raceway types. You’ll find each of the nine family members defined in Art. 100, and each of them has a Chapter 3 Article with the requirements for using it. Only two of them are metallic: intermediate metal conduit (IMC) and rigid metal conduit (RMC). It’s worth noting that IMC is stronger and lighter than RMC.
Why do these have Chapter 3 Articles? The title of Chapter 3 is Wiring Methods and Materials. Raceway does not have a Chapter 3 Article because it’s not a specific wiring method or material.
Rather than use a generic term such as “conduit” in reference to a particular raceway, it’s better to use the specific name of that particular raceway. So what are the raceway types, and where do you find the requirements for them?
If you go to the Table of Contents of the NEC and look at what’s in Chapter 3, you’ll notice a series of Articles pertaining to specific types of cables. It runs from Art. 315 (MV Cable) through Art. 340 (Type UF). Right after this, the NEC starts with the raceways.
There are four groupings of raceway types:
  1. Conduits. This series runs from 342 (IMC) through 356 (LFNC).
  2. Tubing: 358, 360, 362. Those are for FMT, EMT, and ENT, respectively.
  3. Gutters and buses. This series runs from 366 through 371.
  4. Miscellaneous. This series covers various types of raceways (e.g., cellular metal floor raceways, strut-type channel raceway, surface metal raceways) and wireways (e.g., metal wireways, nonmetallic wireways). This series runs from 372 through 390, but it’s punctuated with some things that don’t quite belong in this grouping (e.g., nonmetallic extensions, multioutlet assemblies) of raceway types.
As you can see, Articles that cover a specific type of raceway combine to make up most of Chapter 3. The sheer number of them tells you something important. When designing a system, ordering materials, or assembling in the shop or field, you must be specific as to which wiring methods and materials you mean. One way this costs money in the field is when someone is using a bender with a shoe that is meant for a different type of raceway. If the shoe doesn’t say EMT on it, don’t use it with EMT. The same goes for RMC/IMC.
Or suppose you text the shop to deliver a box of “3/4 conduit couplings” to the job site. The next morning, you’re standing there with several sticks of EMT cut and bent, only to find the shop sent you fittings for IMC. Who made the error here? It can easily happen the other way around. You text that you need a box of “3/4 conduit couplings.” The next morning, you’re standing there with several sticks of IMC cut, threaded, and bent. But the box has EMT fittings because the runner didn’t know the difference. There’s no parts bin labeled “conduit couplings” because conduit is a generic term. The box will say IMC couplings or EMT couplings because those are specific names for specific things.
Chapter 9 of the NEC — Part 5